    Question R404A Compressor In Deep Icing







    Why & how does this happened to the compressor?

    Please give me an answer.. Thanks



  2. #2
    Join Date
    Nov 2009
    Location
    Western PA
    Age
    48
    Posts
    69
    Rep Power
    15

    Re: R404A Compressor In Deep Icing

    Well, obviously, the portions that have ice covering them are below 32 degrees F.

    Whether or not that is a problem would require mor information.

    The one that is a bit concerning to me is the photo of an icy line from what appears to be an oil separator. That, I think, is a problem.

    Otherwise, what is the evpa temp and superheat and we can give a bit more informed answer.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: R404A Compressor In Deep Icing

    If the oil return pipe is covered with ice, it means that the compressor is pumping liquid!!!!

    Something is very wrong there, it could be defrosting with LSV open.

    Start collecting details: Refrigerant? Working temp? Suction and discharge pressure? What parts are along the pipes and do function properly?

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: R404A Compressor In Deep Icing

    Hi Shaman

    Looks like it is getting liquid refrigerant returning to the compressor, needs suction pressure and temperature to work out superheat to be sure, i expect the discharge pipe is quite cool to the tough as well, it looks quite bad in the pictures , maybe low load on the evaporator, faulty expansion device, solenoid, wrong refrigerant etc etc

    I'm wondering, if it is pumping liquid, that this is then making its way to the oil seperator and causing the float to open as the level rises and work as expansion device, hence the frost on the pipe from the bottom of the seperator.

    Running like this will wash oil from the bores and bearings and shorten the life of the compressor.

    Jon

  5. #5
    Join Date
    Apr 2009
    Location
    Singapore
    Age
    48
    Posts
    17
    Rep Power
    0

    Re: R404A Compressor In Deep Icing

    The R404A Compressor -

    => Discharge Pressure is 220 psi
    => Suction Pressure is 15 psi
    => Working Temp is -30*C

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: R404A Compressor In Deep Icing

    Quote Originally Posted by shaman View Post
    The R404A Compressor -

    => Discharge Pressure is 220 psi
    => Suction Pressure is 15 psi
    => Working Temp is -30*C
    and your superheat, sub-cooling etc readings are ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    johnlly's Avatar
    johnlly Guest

    Re: R404A Compressor In Deep Icing

    I think something is wrong in the system. if the temperature of evaprator is too low,you can deforst first .maybe any liquid pipe valve reture to the compresor is leaking.

  8. #8
    Eng_pius's Avatar
    Eng_pius Guest

    Re: R404A Compressor In Deep Icing

    is the gas level ok?

  9. #9
    Eng_pius's Avatar
    Eng_pius Guest

    Re: R404A Compressor In Deep Icing

    check to see if there are any leaks

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: R404A Compressor In Deep Icing

    Quote Originally Posted by johnlly View Post
    I think something is wrong in the system. .
    Good observation....

  11. #11
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: R404A Compressor In Deep Icing

    wouldnt happen to be the liquid line feeding what i think is an oil seperator
    mmm to beer or not to beer...........lets drink breakfast

Similar Threads

  1. Max low side pressure in R404A system
    By Wilade in forum Technical Discussions
    Replies: 8
    Last Post: 25-08-2009, 09:23 PM
  2. Accidentally mixed R404A with R134a
    By toma in forum Trouble Shooting
    Replies: 1
    Last Post: 13-08-2008, 03:33 PM
  3. R507 to R404a
    By Andy AC in forum Commercial
    Replies: 2
    Last Post: 09-08-2008, 05:36 PM
  4. Why not R404a?
    By afak in forum Technical Speculations
    Replies: 12
    Last Post: 02-04-2007, 08:58 PM
  5. R134a or R404a
    By jingua_ph in forum Refrigerants
    Replies: 4
    Last Post: 27-09-2006, 03:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •