Thread: R404A Compressor In Deep Icing
-
27-12-2009, 11:02 AM #1
R404A Compressor In Deep Icing
Why & how does this happened to the compressor?
Please give me an answer.. Thanks
-
27-12-2009, 02:55 PM #2
Re: R404A Compressor In Deep Icing
Well, obviously, the portions that have ice covering them are below 32 degrees F.
Whether or not that is a problem would require mor information.
The one that is a bit concerning to me is the photo of an icy line from what appears to be an oil separator. That, I think, is a problem.
Otherwise, what is the evpa temp and superheat and we can give a bit more informed answer.
-
27-12-2009, 04:00 PM #3
Re: R404A Compressor In Deep Icing
If the oil return pipe is covered with ice, it means that the compressor is pumping liquid!!!!
Something is very wrong there, it could be defrosting with LSV open.
Start collecting details: Refrigerant? Working temp? Suction and discharge pressure? What parts are along the pipes and do function properly?
-
27-12-2009, 04:11 PM #4
Re: R404A Compressor In Deep Icing
Hi Shaman
Looks like it is getting liquid refrigerant returning to the compressor, needs suction pressure and temperature to work out superheat to be sure, i expect the discharge pipe is quite cool to the tough as well, it looks quite bad in the pictures , maybe low load on the evaporator, faulty expansion device, solenoid, wrong refrigerant etc etc
I'm wondering, if it is pumping liquid, that this is then making its way to the oil seperator and causing the float to open as the level rises and work as expansion device, hence the frost on the pipe from the bottom of the seperator.
Running like this will wash oil from the bores and bearings and shorten the life of the compressor.
Jon
-
28-12-2009, 11:40 AM #5
Re: R404A Compressor In Deep Icing
The R404A Compressor -
=> Discharge Pressure is 220 psi
=> Suction Pressure is 15 psi
=> Working Temp is -30*C
-
28-12-2009, 12:06 PM #6
-
28-12-2009, 01:09 PM #7
Re: R404A Compressor In Deep Icing
I think something is wrong in the system. if the temperature of evaprator is too low,you can deforst first .maybe any liquid pipe valve reture to the compresor is leaking.
-
02-01-2010, 09:11 AM #8
Re: R404A Compressor In Deep Icing
is the gas level ok?
-
02-01-2010, 09:12 AM #9
Re: R404A Compressor In Deep Icing
check to see if there are any leaks
-
02-01-2010, 01:29 PM #10
-
03-01-2010, 10:37 PM #11
Re: R404A Compressor In Deep Icing
wouldnt happen to be the liquid line feeding what i think is an oil seperator
mmm to beer or not to beer...........lets drink breakfast
Similar Threads
-
Max low side pressure in R404A system
By Wilade in forum Technical DiscussionsReplies: 8Last Post: 25-08-2009, 09:23 PM -
Accidentally mixed R404A with R134a
By toma in forum Trouble ShootingReplies: 1Last Post: 13-08-2008, 03:33 PM -
R507 to R404a
By Andy AC in forum CommercialReplies: 2Last Post: 09-08-2008, 05:36 PM -
Why not R404a?
By afak in forum Technical SpeculationsReplies: 12Last Post: 02-04-2007, 08:58 PM -
R134a or R404a
By jingua_ph in forum RefrigerantsReplies: 4Last Post: 27-09-2006, 03:31 PM