    Oct 2009
    Syria
    45
    low oil temperature
    hi dear sirs
    we got a problem and we wish you help us
    we have a HC-DPCU consists of a MYCOM-SCV screw compressor, oil separator equipped with an electric oil heater, air cooler as a condenser, refrigerant receiver, flash tank as an economizer and a kittle-type chiller as evaporator.
    the refrigerant is propane
    the problem is:
    oil heater is broken, so during the night work, oil temperature goes below 25 degree c that leads to shut-down the unit.
    ambient temperature during night is 15 degree c
    so, is there any way to increase the oil temperature?
    thank you all
    11,025
    Re: low oil temperature
    Replace broken oil heater.
    3,356
    I'm assuming compressor is running when oil tempreture is low .
    What type of oil cooler or cooling do you have ?
    If you can control this it will help .
    Sump heater is usually only used when compressor is off , but it should be fixed regardless .
    Oct 2009
    Syria
    45
    Hi dear RANGER1
    You are right
    when the compressor is on, the oil temperature goes below (25C) SO, i have a trip.
    we use the liquid propane downstream the propane receiver to cool the oil but the control valve on the liquid propane line does'nt open until the oil temperature becomes (50C) or higher so, we dont have oil cooling when the oil teperature is below (50C).
    propane vapor enters the suction line of the compressor at (-8C), suction line pressure is (2.8 - 3bars), compressor discharge pressure is (9-10 bars).
    what it drives me crazy is:
    at the same discharge pressure the oil temperature decreases gradualy during night.
    sorry if i'm bothering you
    thank you very much
    Dec 2006
    Iran
    43
    55
    Dear sir,
    why Dont you replace the broken oil heater? if hte compressor work with tis oil temp. lead to compressor damage and it cost more than a oil heatrer.
    by the way you should keep oil tempreture around 45~50 degree of centigrad.
    bye.
    Jan 2006
    Croatia
    68
    2,261
    31
    Hi, reyad-saleh
    Quote Originally Posted by reyad-saleh View Post
    hi dear sirs
    the problem is:
    thank you all
    If you start your compressor even with cold oil ... I assume you can get that permission ... then oil must be enough warm/hot after few minutes to run compressor without any problem day or night ... usually during compressor run oil heater is off ...
    seems there is some other problem within your plant ...
    what is your alarm????
    .... low oil temp ....
    .... low oil pressure ...
    ... or something else ...
    .... to give some answers we need more input data ... like this we are guessing and maybe leading you in wrong way ...
    Best regards, Josip
    s1goon's Avatar
    s1goon Guest
    hi dear sirs
    the problem is:
    thank you all
    u should replace the oil heater otherwise the unit will trip low oil temp be compressor start.
  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  3. LG heat pump problem
    By back2space in forum Heat Pumps
    Last Post: 01-02-2009, 11:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Last Post: 05-12-2007, 06:25 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Last Post: 20-05-2003, 12:27 AM