low oil temperature
hi dear sirs
we got a problem and we wish you help us
we have a HC-DPCU consists of a MYCOM-SCV screw compressor, oil separator equipped with an electric oil heater, air cooler as a condenser, refrigerant receiver, flash tank as an economizer and a kittle-type chiller as evaporator.
the refrigerant is propane
the problem is:
oil heater is broken, so during the night work, oil temperature goes below 25 degree c that leads to shut-down the unit.
ambient temperature during night is 15 degree c
so, is there any way to increase the oil temperature?
thank you all
-
26-12-2009, 11:24 AM #2
Re: low oil temperature
Replace broken oil heater.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
26-12-2009, 09:35 PM #3
Re: low oil temperature
I'm assuming compressor is running when oil tempreture is low .
What type of oil cooler or cooling do you have ?
If you can control this it will help .
Sump heater is usually only used when compressor is off , but it should be fixed regardless .Last edited by RANGER1; 26-12-2009 at 11:13 PM.
-
02-01-2010, 09:48 PM #4
Re: low oil temperature
Hi dear RANGER1
You are right
when the compressor is on, the oil temperature goes below (25C) SO, i have a trip.
we use the liquid propane downstream the propane receiver to cool the oil but the control valve on the liquid propane line does'nt open until the oil temperature becomes (50C) or higher so, we dont have oil cooling when the oil teperature is below (50C).
propane vapor enters the suction line of the compressor at (-8C), suction line pressure is (2.8 - 3bars), compressor discharge pressure is (9-10 bars).
what it drives me crazy is:
at the same discharge pressure the oil temperature decreases gradualy during night.
sorry if i'm bothering you
thank you very much
-
05-03-2010, 08:36 PM #5
Re: low oil temperature
Dear sir,
why Dont you replace the broken oil heater? if hte compressor work with tis oil temp. lead to compressor damage and it cost more than a oil heatrer.
by the way you should keep oil tempreture around 45~50 degree of centigrad.
bye.
-
05-03-2010, 10:30 PM #6
Re: low oil temperature
Hi, reyad-saleh
If you start your compressor even with cold oil ... I assume you can get that permission ... then oil must be enough warm/hot after few minutes to run compressor without any problem day or night ... usually during compressor run oil heater is off ...
seems there is some other problem within your plant ...
what is your alarm????
.... low oil temp ....
.... low oil pressure ...
... or something else ...
.... to give some answers we need more input data ... like this we are guessing and maybe leading you in wrong way ...
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
06-03-2010, 12:55 PM #7
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
LG heat pump problem
By back2space in forum Heat PumpsReplies: 132Last Post: 01-02-2009, 11:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM