    ELCB case



    Hi all,

    We installed the carrier 38LZA100-10 nos, and installation caltalouge request the MOCP 63A.So we installed the MCB 63A then ELCB 63A .But MCB is not trip and ELCB is trip the starting time.I don't know "why that ELCB trip?" and that ELCB on write 300mA.What that mean?



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: ELCB case

    In a few words a MCB protects against maximum total current ELCB and RCD protect against current that goes astray (not where it is suposed to go) this bit that goes to the wrong place should be very small (mA), so you have some electricity going to earth. It could be a major fault, but more than likely being new it is moisture in the electrical components.
    First test witha multi-meter (low voltage) resistance (ohms), if you this does not show anything, then more than likely moisture. Disconnect all electronics, then test motors and heaters with a megga (high voltage).
    If all OK then ELCB could be faulty

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ELCB case

    There have been a few discussions on this subject before.

    ELCB are to protect people and are not suitable for protecting refrigeration machines.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: ELCB case

    Earth Leakage Circuit Breaker or ELCB, is to protect us from getting electric shocks [it defenatly not used on Electric Chairs....]

    Nany industrial machinary have small earth leakage so the use of such protection will not allow to operate such machinary.

    300 mA is the currant that activate it.

    Each machine comes with MCB to protect the components from excesive curant.

    The extra MCB you were asked to install is to protect the main electric cabe, 16 mm3 in 63A case.

  5. #5
    Join Date
    Dec 2009
    Location
    Myanmar
    Age
    40
    Posts
    6
    Rep Power
    0

    Re: ELCB case

    we tested the megga, is ok and we found the voltage is not stable 380 V to 360 V running.eg, Voltage is 380 V have and we run the one unit , if start the compressor,voltage is going down to 370 V.So I think ELCB is trip for voltage variable?

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: ELCB case

    Quote Originally Posted by myohantun View Post
    we tested the megga, is ok and we found the voltage is not stable 380 V to 360 V running.eg, Voltage is 380 V have and we run the one unit , if start the compressor,voltage is going down to 370 V.So I think ELCB is trip for voltage variable?
    ELCB does not protect against this, when you used your megga did you test the whole unit or each individual part?

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: ELCB case

    Quote Originally Posted by myohantun View Post
    we tested the megga, is ok and we found the voltage is not stable 380 V to 360 V running.eg, Voltage is 380 V have and we run the one unit , if start the compressor,voltage is going down to 370 V.So I think ELCB is trip for voltage variable?
    hi,myoha..,your this statement is against your first report.make it clear that,
    1.is your system tripping at starting on ELCB?
    2.is your system tripping after starting the 2nd compressor
    3.what is the meg.value?
    (as system tripping the on ELCB AT STARTING,YOU WILL NOT GET CHANCE TO CHECK THE VOLTAGE)

    MOIDEEN-DUBAI

  8. #8
    Join Date
    Dec 2009
    Location
    Myanmar
    Age
    40
    Posts
    6
    Rep Power
    0

    Re: ELCB case

    Thanks for your reply? We done megga test is CDU only, so we will test again FCU.
    And reply to u..
    Best regards,

  9. #9
    Join Date
    Dec 2009
    Location
    Myanmar
    Age
    40
    Posts
    6
    Rep Power
    0

    Re: ELCB case

    Thanks moideen,

    1.I installed FCU is 16 Tons and CDU is 8 tons (2 nos)combine.Each CDU RLA is 22 A.
    We operate the system, FCU is running ok and first CDU is start running ( that ok ) and second CDU start operate but that CDU ELCB is trip.
    So, we change the sequent CDU ( 2 nos )
    But Last operate CDU's ELCB are trip.I don't think so. Pls provide for that problem.
    Best regards,
    myohantun

Similar Threads

  1. crank case heaters in scroll compressors
    By abbasi in forum Fundamentals
    Replies: 19
    Last Post: 03-08-2010, 03:04 AM
  2. Isa Gelato Case at -18
    By Gridley13 in forum Commercial
    Replies: 16
    Last Post: 05-04-2010, 12:06 AM
  3. a frozen book display case
    By tempo in forum Technical Discussions
    Replies: 3
    Last Post: 15-08-2008, 07:20 PM
  4. cpc case controller
    By dingo in forum Trouble Shooting
    Replies: 4
    Last Post: 09-04-2008, 09:35 AM
  5. Two temperature display case with low suction presure
    By kengineering in forum Supermarket Refrigeration
    Replies: 11
    Last Post: 05-03-2007, 02:13 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •