Help required - York chiller YDAJ77
We have developed a problem with our YDAJ77XT9 York Millenium Recip chiller system. We currently operate only systems 1 & 2 (systems 3 and 4 have been out of action for years, but we don't need more than two systems).
Our setpoint for water leaving temp is -5C (30% glycol), but we are unable to achieve it because system 2 will not kick in. When system 1 runs as lead compressor (normal operation), we get a "NO COOLING LOAD" message and the system refuses to start then gives us a low oil pressure error. We changed the lead to system 2 to see what would happen and it again refused to start, giving a low oil pressure message. System 1 started shortly afterwards. Systems 1's pressure look to be fine, but system 2 is obviously not giving us anything useful as it is not starting. I believe that the solenoid activates, but the compressor doesn't receive the start signal.
Our service engineers seem to think the problem is related to one of the circuit boards, but our control engineer is convinced that the compressor itself is the problem. If it is indeed the circuit board, we don't know how to determine whether it is the main EPROM board or one of the subsidiary boards.
Can anyone offer any advice as to likely cause, possible solutions and, if the boards are the problem, how to diagnose which one it is?
Thanks in advance.
-
24-12-2009, 01:32 PM #2
Re: Help required - York chiller YDAJ77
The history buffer is a good place to start, is the compressor actually starting, if the micro controller outputs a start signal to the compressor it looks for a current feedback > 7A and an oil PD > 2Barg within 30 secs. The micro outputs to a relay card mounted adjacent to the comp contactors, these do have a tendancy to arc so may be an idea to check these as well.
-
25-12-2009, 11:31 AM #3
Re: Help required - York chiller YDAJ77
we get a "NO COOLING LOAD" message and the system refuses to start then gives us a low oil pressure error.
-
31-12-2009, 08:51 AM #4
Re: Help required - York chiller YDAJ77
Hi Yuri, many thanks for correcting my timing mistake.
As one of the old York factory boys I worked on the YCAJ / YDAJ assembly line with all European designated chillers, (those built in the Basildon factory) all having CT(s) fitted.
We did have a couple of USA built units come through that didn't have CTs' installed but these went to the far east, (no BS or CE certification).
-
31-12-2009, 10:03 AM #5
Re: Help required - York chiller YDAJ77
Hi scut,this chiller is a master and slave model,check your rate of sensitivity default try to adjust the temprature weather can run the system if this system run try to rectify low oil pressure problem weather need to do overhaul compressor
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
York Chiller Manual Required
By cool_mariner in forum Air ConditioningReplies: 10Last Post: 19-11-2010, 09:30 AM -
York Chiller startup when on Emergency Power
By Apollo10 in forum Trouble ShootingReplies: 3Last Post: 22-12-2008, 07:13 PM -
york chiller motor rotation error
By cesarnino in forum Trouble ShootingReplies: 7Last Post: 13-12-2008, 03:43 PM -
York Chiller help required
By RAVISEKAR in forum CommercialReplies: 9Last Post: 17-05-2008, 12:57 PM