    Post Compressor Not turning off on defrost



    Hoover Fridge/Freezer, 480lt, quite old, orchid range. Recently fitted an Embraco Compressor FG95HAK. When the defrost timer goes into 'DEFROST' mode, evaporator fan turns off but compressor doesnt. I suspect wiring to be wrong. The panel on the compressor has connections labelled L2, L1, N, Earth, in that order. At the moment I have 2 brown lines (one from mains and one from defrost timer) connected to L2. On L1 I have 0ne black line which I suspect is from thermo. Neutral no problem, two blue from mains and timer. I am confident the timer is ok. Gassing should be ok too. She gets cold but the frost and ice build up due to continuous compressor run.
    WHAT COULD BE THE PROBLEM???



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Compressor Not turning off on defrost

    Quote Originally Posted by Thommo View Post
    Hoover Fridge/Freezer, 480lt, quite old, orchid range. Recently fitted an Embraco Compressor FG95HAK. When the defrost timer goes into 'DEFROST' mode, evaporator fan turns off but compressor doesnt. I suspect wiring to be wrong. The panel on the compressor has connections labelled L2, L1, N, Earth, in that order. At the moment I have 2 brown lines (one from mains and one from defrost timer) connected to L2. On L1 I have 0ne black line which I suspect is from thermo. Neutral no problem, two blue from mains and timer. I am confident the timer is ok. Gassing should be ok too. She gets cold but the frost and ice build up due to continuous compressor run.
    WHAT COULD BE THE PROBLEM???

    It sounds like you have the live conected to the comp supply, resulting in the comp running all the time. Re check the conections and make sure your feed from the stat feeds the comp.

    Should not be hard just check and swap the lives over.

    Cheers taz.

  3. #3
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Compressor Not turning off on defrost

    Welded contact in the defrost timer? (The previous compressor drew exessive el. current).

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Defrost settings for Daikin RY100F+ FHYB100
    By rdepoort in forum Air Conditioning
    Replies: 2
    Last Post: 21-12-2009, 05:38 PM
  3. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  4. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM
  5. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •