    Discharge pressure going very high in few seconds



    system dischare pressure is going high and tripping in high discharge pressure with in 30seconds in aircooled chiller so request your help



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Discharge pressure going very high in few seconds

    Restriction in high side.

    If you provide more data you will get more precise answer.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Discharge pressure going very high in few seconds

    As Nike said - restriction on HP side. Blocked check-valve?

    Alternatively, if condenser fan stopped - no cooling. We see this in heat-pumps, if the condenser water flow is turned off, for instance.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Discharge pressure going very high in few seconds

    has it got a CPR fitted ?[crankcase pressure regulator],if it has try ajusting it to set the back pressure and that will in turn control the discharge pressure.if not fit one,obviousley dont restrict the overhall duty required.

  5. #5
    Join Date
    Feb 2010
    Location
    N.Ireland
    Posts
    16
    Rep Power
    0

    Re: Discharge pressure going very high in few seconds

    stating the obvious but check discharge service valve fully open also that air cooled condenser clear?

  6. #6
    Join Date
    Mar 2010
    Location
    australia
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: Discharge pressure going very high in few seconds

    nitrogen in system will have this affect

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Discharge pressure going very high in few seconds

    ^ Very much so.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Discharge pressure going very high in few seconds

    condencer fans running ? righ way?

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Discharge pressure going very high in few seconds

    30 seconds is a long time, partially restricted is more likely.
    Too much refrigerant will get you high head pressure.

    you did not supply any details on what your machine does and the operating and control procedure so trying to guess is like playing darts...

    Please try to bring us a better picture of the system.
    Photos always help.

  10. #10
    Join Date
    Mar 2010
    Location
    United states
    Age
    66
    Posts
    5
    Rep Power
    0

    Re: Discharge pressure going very high in few seconds

    Chech to see if non condensibles are in the system.

  11. #11
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: Discharge pressure going very high in few seconds

    no question is stupid but how can you check if there are non-condesable in the system? Is there a trick, I would like to be enlightend and I am not sarcastic at all, ty.

  12. #12
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Discharge pressure going very high in few seconds

    Quote Originally Posted by Royal241 View Post
    no question is stupid but how can you check if there are non-condesable in the system? Is there a trick, I would like to be enlightend and I am not sarcastic at all, ty.
    If you have non condensables, they sit in the top of the condenser, stopping flow of the refrigerant to that part of the condenser. So you tend to find that the Top of the condenser is "cooler" than the rest!

  13. #13
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Discharge pressure going very high in few seconds

    Quote Originally Posted by Royal241 View Post
    no question is stupid but how can you check if there are non-condesable in the system? Is there a trick, I would like to be enlightend and I am not sarcastic at all, ty.
    Shut the machine down let it equalize to ambient temp and with P/t chart take readings from gauges should be same as ambient if no non condesibles present
    My wife used to say you never listen to a word I say at least I think that what she said

  14. #14
    Join Date
    Sep 2008
    Location
    Newcastle upon tyne
    Age
    75
    Posts
    80
    Rep Power
    16

    Re: Discharge pressure going very high in few seconds

    Hi
    Another trick with non condensibles is a portable purge unit.

    We have 1 which we put on R123/R11 units to aid purging after nitrogen tests or units purge defective.

    It is suitable to work on most refrigerants and is pre programmed in the software.

    Depends on size of unit and access points available.

    AWW

  15. #15
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Discharge pressure going very high in few seconds

    More details on the system is better.It could be anything.Restriction,non condensible,lack of air flow etc.

  16. #16
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: Discharge pressure going very high in few seconds

    first of all you check your condenser it my be scaled. descaled it from descaler. if your condenser is water cooled then you can applay this mathod.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Discharge pressure going very high in few seconds

    Leave him guys, one of the so many who come here, asks a question and never come back.
    I call this lack of elementary good manners.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Discharge pressure going very high in few seconds

    Peter 1.. good one, just leave him guys.

  19. #19
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Discharge pressure going very high in few seconds

    not operate fans, fan rotation correct?

  20. #20
    Join Date
    Sep 2008
    Location
    Canada
    Age
    42
    Posts
    12
    Rep Power
    0

    Re: Discharge pressure going very high in few seconds

    txv too closed on a critical charged system ?

Similar Threads

  1. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  2. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  3. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  4. cooling &freezing comp.
    By afeef in forum Industrial Compressors
    Replies: 25
    Last Post: 15-12-2006, 09:29 PM
  5. Replies: 6
    Last Post: 18-11-2005, 04:30 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •