    Smile Exapansion for Cascade system



    I have a project cascade system -60 degrees C bolt use refrigeran R-23 ( low Satage) and second refrigean R-404 (two stage) , i want to ask expasi valve type R-23 for cascade system of -60 degrees C. Thanks



  2. #2
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    189
    Rep Power
    15

    Re: Exapansion for Cascade system

    I haven't worked with R-23 in many years, it is just about the holidays but when I get back I am certain I can provide some information. Why R-23? it runs higher pressure and temperature then R-508B or R-13.
    Also if you speak to a expansion valve manufacturer I have found that they will almost always recomend a valve for your application.

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Exapansion for Cascade system

    what is the capacity of low side in kw ? TEX mfr can support you in the selection of valve for R-23 like Sporlan, danfoss, alco etc . They can guide you .

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Exapansion for Cascade system

    Besides, you need an oil separator which is efficient 99% in r-23 system. Such applications are frought with oil return difficulties to compressor . Borosilicate microfibre type oil separator would be a good idea . Many systems are failure prone in the absence of a good separator ; conventional ones would not do a good job of oil return.compressor failures are frequent .

  5. #5
    Join Date
    Jan 2009
    Location
    Bangkok
    Age
    48
    Posts
    21
    Rep Power
    0

    Re: Exapansion for Cascade system

    You can use a electronic expansion valve from Danfoss is AKV model.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. Ammonia Heat Pumps
    By US Iceman in forum New Technologies
    Replies: 39
    Last Post: 22-03-2010, 07:36 PM
  3. Enthalpy Increasing Buffer System
    By Reflexive in forum Technical Speculations
    Replies: 3
    Last Post: 23-12-2008, 04:18 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Replies: 8
    Last Post: 31-03-2007, 05:34 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •