    This is why you should change your filter driers...
    This is a photograph of the inside of a suction line on an R-22 hydro-chiller plant. Apparently they have a broken chiller that has been leaking water into the refrigerant side... I was told that the operating engineers got tired of changing the filter drier cores so they just stopped putting them in the housing instead of finding out why they were plugging up in the first place!
    Mar 2009
    KZN, South Africa
    58
    2,212
    14
    Re: This is why you should change your filter driers...
    Wow...
    That's a pretty remarkable picture.
    Aug 2005
    5,327
    Looks like the inside of a cold trap.
    If the chiller tubes are leaking they could change cores every hour and it would not dry the system!
    Aug 2007
    Seattle, WA. USA
    26
    It just amazes me that the guys running this plant didn't notice that there was a problem the first time they had to change the cores. An R22 system that runs at 25F SST usually is not going to have a moisture infiltration problem. I heard after I posted this that they had removed all the expansion valves from the system, installed a low side pump separator, and installed hand expansion valves because they couldn't get the TXV's to feed. The ultimate band-aid for a broken chiller but even that eventually didn't solve their problem...
    Aug 2005
    5,327
    Quote Originally Posted by lloydjosang
    ...and installed hand expansion valves because they couldn't get the TXV's to feed.
    Don't think it had anything to do with the water do you?
    Who in the world told them to do that? That's nuts...
  1. GAH filter driers
    By djbe in forum Transport
    Last Post: 29-07-2010, 08:11 PM
  2. Remove Suction Filter Elements??
    By ChillTechnican in forum Fundamentals
    Last Post: 12-12-2009, 06:54 PM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Last Post: 10-09-2009, 01:45 AM
  4. Filter dryer question.
    By wingman in forum Technical Discussions
    Last Post: 21-05-2009, 02:52 PM
  5. Suction Filter colapse
    By R. skiffington in forum Trouble Shooting
    Last Post: 04-10-2008, 09:10 PM