Thread: McQuay MCK050 error codes???
-
21-12-2009, 10:05 PM #1
McQuay MCK050 error codes???
Hey all,
Hope someone can come up with an answer,
I have a McQuay MCK050 Cassette on R407c
with there SLM3 remote control showing an
E4 Error during the heating cycle,
Any ideas??
-
22-12-2009, 06:04 AM #2
Re: McQuay MCK050 error codes???
Look inside the filter probably there is show alarm codes. What is the outside temperature ?Maybe cant make the defrost cycle or is too cold outside.
-
22-12-2009, 07:57 AM #3
Re: McQuay MCK050 error codes???
Radiohead,
E4 = Compressor overload.
Cycle power off / on. Check all connections, filter, refrigerant charge etc,
Good luck.
-
23-12-2009, 08:55 AM #4
Re: McQuay MCK050 error codes???
Hey Baycuclaudyu,
Outside temps are going from +3 to -2c
the system fault seems to effect the unit after it has been on for some time,
so could be a defrost problem,
Can the defrost time \ temp limit be extended to help clear a build up on the outdoor unit??
-
23-12-2009, 08:58 AM #5
Re: McQuay MCK050 error codes???
Hi MQFS OZ,
Thanks for the reply, going to run through a few of these on site later,
will let ya know how it goes.
-
23-12-2009, 10:35 PM #6
Re: McQuay MCK050 error codes???
Radiohead,
Also check all sensors for shorts and lose connections. If the unit has a phase protection board with a discharge temp sensor the system may have faulted on high discharge temp.
Regards MQFS OZ
Similar Threads
-
McQuay Centrifugal Oil pressure
By setrite in forum Trouble ShootingReplies: 10Last Post: 13-01-2011, 01:17 PM -
McQUAY CHILLERS...
By DoD in forum CommercialReplies: 44Last Post: 10-12-2010, 05:21 PM -
Aaaargh Mcquay!!!
By pb smash in forum ElectricalReplies: 13Last Post: 11-02-2010, 03:27 PM -
Mcquay Chiller problem
By hitmanzak in forum Trouble ShootingReplies: 2Last Post: 23-08-2009, 07:03 PM -
McQuay ALS F XE273.2 990Kw, highest return temp?
By THE WOMBAT in forum Technical SpeculationsReplies: 1Last Post: 07-08-2009, 10:59 AM