    Help with discharge line



    Hi everybody:

    I have a system with the following characteristics:
    • Single stage
    • Ammonia
    • Screw compresors
    • T evap = -21 ªC
    • T Cond. = +35ºC
    • Compressor's capacity = 1395Kw
    • Condenser's Capacity = 2047 Kw
    The actual discharge line is 4" and I was thinking to change it for 5". i would like to know your opnion about this. somebody could tell me if there are some rule for sizing the discharge line or what happens if i don't change nothig. i hope you can help me

    Best Regards.

    Luis Sandoval.



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Help with discharge line

    Quote Originally Posted by luissandoval View Post
    Hi everybody:


    I have a system with the following characteristics:
    • Single stage
    • Ammonia
    • Screw compresors
    • T evap = -21 ªC
    • T Cond. = +35ºC
    • Compressor's capacity = 1395Kw
    • Condenser's Capacity = 2047 Kw
    The actual discharge line is 4" and I was thinking to change it for 5". i would like to know your opnion about this. somebody could tell me if there are some rule for sizing the discharge line or what happens if i don't change nothig. i hope you can help me

    Best Regards.

    Luis Sandoval.

    I would ask why?

    Why do you want to change the discharge line.
    Is the ststem not working?

    Cheers taz.

    .

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Help with discharge line

    The rule is: how much pressure drop is there and can you live it? Each value of pressure loss translates into an equivalent temperature loss. The temperature loss affects the saturated condensing temperature.

    Therefore, if you keep the saturated discharge temperature (at the compressor) at say 95°F (35°C) the condensing temperature will be lower. Is the condenser heat rejection rated for the lower condensing temperature?

    On the other hand, if the condensing temperature is 95°C (35°C), then the saturated discharge temperature will be higher. The latter one is how I look at this. Otherwise, the condenser must be larger for the lower condensing temperature.
    If all else fails, ask for help.


  4. #4
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: Help with discharge line

    i'm worry about the velocity in the discharge line because it's so so 22.5 m/s i don't sure if this pipe will work ok with this velocity.

    Luis

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Help with discharge line

    Two concerns.


    1. High velocity = higher pressure loss.
    2. Higher velocity = greater concern for liquid hammer if condensate is inside pipe (gas condensing).

    If you can ensure you will not have gas condensation in the discharge line then the main concern is the pressure loss and affect it has on saturation temperatures.
    If all else fails, ask for help.


  6. #6
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: Help with discharge line

    Luis
    I think you should figure out the pressure drop and temperatura drop.
    I made a preliminare calculation with 20 m long pipe/4 elbow, 2 Globe valve and a I get 0,133 bar pressure loss and 0,344 ºC (no condenser pressure drop).
    Look in the compressor curve how much power you will low with 5 in pipe.
    The next question will be: will the power reducction payback the new pipe?

    Hope this help take a desition
    regards
    Gwapa

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Oil in discharge line
    By chillyblue in forum Trouble Shooting
    Replies: 18
    Last Post: 30-10-2008, 06:52 AM
  3. Oil Leak in NH3 Discharge Line Flange
    By NH3LVR in forum Industrial
    Replies: 9
    Last Post: 26-05-2007, 09:15 PM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •