    Question The condenser is 15 metres below the compressor?



    Will I find technical documentations about making the cooling installation where, where the condenser is 15 metres below the compressor?
    How to make the return of oil on the liquid?
    What are there problems with the return of oil?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: The condenser is 15 metres below the compressor?

    Whereabouts is the evaporator?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2009
    Location
    St-ce
    Posts
    26
    Rep Power
    0

    Re: The condenser is 15 metres below the compressor?

    The evaporator is 1 the metre over the compressor - precise air conditioner.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: The condenser is 15 metres below the compressor?

    Oil won't be a problem as the liquid will carry it easily.

    The problem would be needing to raise the high side pressure in order to lift the liquid back up to the evaporator.

    This would be a good system to add a liquid pump.

Similar Threads

  1. Clean Condenser Running too hot??
    By Chseybold in forum Trouble Shooting
    Replies: 81
    Last Post: 03-01-2010, 11:50 PM
  2. Energy/power saving compressor application
    By Apel in forum Technical Discussions
    Replies: 3
    Last Post: 02-07-2008, 04:30 AM
  3. compressor higher than condenser
    By agrab76 in forum Technical Discussions
    Replies: 2
    Last Post: 06-05-2008, 04:25 AM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. compressor exceeding LRA
    By mush in forum Industrial Compressors
    Replies: 5
    Last Post: 09-01-2008, 05:01 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •