I can confirm the pre heat logo comes on during this problem. Would this mean the short cycling is not likely the cause?? He did say with 4 indoor units on (out of 10) the cycling happend less frequently.He did not have full access to all 10 rooms -hotels eh?
Sadly I attempted to buy a checker from a friend of a regular here. All was agreed until he stopped answering my call(s)..not too sure what went wrong there...
-
17-12-2009, 10:35 AM #2
-
17-12-2009, 10:57 AM #3
-
21-12-2009, 11:24 AM #4
-
21-12-2009, 04:50 PM #5
Re: Daikin VRV 3 pipe changing mode
Crumbs we are having so much trouble on that site it's not funny
On another system they have been waiting for a new inverter compressor. That had a U4 error over the weekend. Our guy went to site, played around checking if all indoors had power on etc. Suddenly it came back on.
Back today to start the reclaim and compressor change but were stopped before starting as another system was not heating properly (historical bad airflow design) + they wanted to have another look at the U4 error (no point changing the compressor if it won't run anyway.)
However half way through that one and a worker noticed oil dripping through the ceiling tile another system had split a liq line! So the compressor/investigation never got started.
The change over system faulting was only noted by the engineer who was looking at another system in error. He mentioned it as a problem but the site guy's are saying they haven't had one complaint from that area so it's being left till we can get the rest sorted...
-
21-12-2009, 09:05 PM #6
Re: Daikin VRV 3 pipe changing mode
Multi,
It sounds like you’ve had one of those days
At least you didn’t need to dig your way through the snow to get up the street on the way home
U4 errors can be real pain on older installs, especially when it’s an intermittent fault.
You will probably be aware of the most common reasons for a U4;
- Mains power off at indoor/bs/outdoor
- Loose live or neutral connection
- Mains power has been switched off/on but system fails when reinitializing (turn power off/on again and hold down reset button for 10sec)
- Bad connection on F1F2 comms lines
- Mice or rats chewing into comms cables!
- If it’s an R22 KJ outdoor unit the small green interface pcb that f1f2 cable connects to has been known to cause probs (not applicabe for 407c).
- Faulty indoor/bs/outdoor main PCB (never had this with intermittent U4 error tho)
- K series units can be very slow to recognize a U4 error
- U4 errors will auto reset when comms are reestablished
Last edited by VRVIII; 21-12-2009 at 09:25 PM.
-
21-12-2009, 09:31 PM #7
Re: Daikin VRV 3 pipe changing mode
Took me 1 1/2 hrs to go 3 miles this afternoon.
We've had rats chew the comms cable in a hotel once and a few of the others here and there. This is a strange one and we can only hope that it holds till Christmas.
The install is only just (and I mean 3 weeks just) 3 years old. It's sad they are failing like this. I won't tell you what the UK facilities Director thinks of Daikin after this and an even worse site up north somewhere....
Just to cheer you back up I am mid swap on a Tosh SHRM: 3 condensers multiplexed and so far in 2 years 3 compressors failed out of 6 !
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Measurement of pipe lengths
By batfink in forum Technical DiscussionsReplies: 11Last Post: 23-09-2008, 09:50 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM