    Hello everybody,
    In chiller with water cooled condenser, compressor oil is collecting into the evaporator. How can we send this oil to the compressor carter? Isthere any solution without changing evaporator?

    Thanks for your helps....

    Aygul

  2. #2
    Join Date
    Jul 2003
    Location
    New Delhi,India
    Age
    58
    Posts
    32
    Rep Power
    0

    Wink Re: collecting oil in evaporator

    Quote Originally Posted by Aygul
    In chiller with water cooled condenser, compressor oil is collecting into the evaporator. How can we send this oil to the compressor carter? Isthere any solution without changing evaporator?
    What the size(TR) of chiller?
    Check the gas it will be short. for temporary solutions

    Is there any unloading system in compressor?

    If yes than unload the compressor all the oil in evaporator will move to compressor.this is temporary solution.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: collecting oil in evaporator

    Hi aygul.

    There are a few solutions.
    You can install an oil sepatator after the compressor.
    You can add a U oil trap on the outlet of the evaporator.
    You can add a little R12 to the refrigerant, it will help oil ruturning.

    Also, check that the TEV is not too open, (superheat too low).

    Can you give some more details of the chiller?

    Chemi

  4. #4
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Re: collecting oil in evaporator

    Quote Originally Posted by aygul
    Hello everybody,
    In chiller with water cooled condenser, compressor oil is collecting into the evaporator. How can we send this oil to the compressor carter? Isthere any solution without changing evaporator?

    Thanks for your helps....

    Aygul
    Hi...is it the case that as oil has collected in the evaporator that someone has been topping up the compressor sump...oil bound evaporator followed by loss of refrigeration effect...loss of suction superheat...I have found that after rectifying the root cause of this type of problem it is reasonably easy to return the oil to the compressor sump where it can be drained to the correct level by running the compressor at full load conditions.There are various reasons to cause oil migration to the evaporator but as other site members have already requested it is necessary to know the details of the unit and a rundown on the present running conditions......best of luck...maybe you could post some details...in any case...the answer is.. no ...you would not have to change the evaporator

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: collecting oil in evaporator

    Is this a new unit and was the problem there since the beginning or is it an old unit which gives just recently problems?
    Own design?
    Did someone changed something?
    Did you serviced always this unit?
    Is there a partial load system on the unit?
    Enough gas in the system?
    Not too high fluctuations in condensing pressure?
    What is the superheat?
    Furthet the same questions as Marc, shell and tube or plate HE and TEV or flooded?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jan 2002
    Location
    turkey
    Age
    54
    Posts
    22
    Rep Power
    0

    Re: collecting oil in evaporator

    Thanks all the answers...

    evaporator is shell and tube type-refrigerant goes through tubes and water goes outside the tubes. Refrigerant is R22, i thing there is enough refrigerant in the system... there is no unloading... there is screw compressor in the system...
    superheat aproximatelly 3 C... tev adjustment is 20 open tours (totally 40 tours)
    I thing i increased superheat closing tev...
    For oil return problem refrigerant velocity is important, when we increase superheat, can we supply to increase refrigerant velocity? or how much can i add R12 into the system?...

    Compressor has oil seperator, can i add additional oil seperator into the system?

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: collecting oil in evaporator

    You're sure the screw has no partial load system (slide on the intake)
    You must be sure and not guess if there is enough refrigerant in the system.
    What about the answers on the other questions we - Chemi,Tejbir, Marc and I - posed you? We need correct answers and no guesses before we hurther can help you.

    A TEV with 20 opening rotations on the spindle doesn't say anything. We need real measured temperature and pressure values.

    You have to know what you're doing if you add R12 in the system, there is no rule to determine the quantity.

    Adding a second oil separator won't help you if the original one had functioned before very well. Is the present one working fine for the moment?

    You see, still too many questions before we can help.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Nov 2004
    Location
    uk
    Age
    77
    Posts
    61
    Rep Power
    20

    Re: collecting oil in evaporator

    Quote Originally Posted by aygul
    Thanks all the answers...

    evaporator is shell and tube type-refrigerant goes through tubes and water goes outside the tubes. Refrigerant is R22, i thing there is enough refrigerant in the system... there is no unloading... there is screw compressor in the system...
    superheat aproximatelly 3 C... tev adjustment is 20 open tours (totally 40 tours)
    I thing i increased superheat closing tev...
    For oil return problem refrigerant velocity is important, when we increase superheat, can we supply to increase refrigerant velocity? or how much can i add R12 into the system?...

    Compressor has oil seperator, can i add additional oil seperator into the system?
    If there is a screw compressor in the system then what type of oil sump and pump is fitted or is there no oil pump at all????..if it was say a Dunham bush horizontal then there are several oil sump and pump configurations.....oil recovery on that type of screw is carried out by adjusting the discharge superheat to a minimum of 18 degrees .....any lower and the oil seperator mesh will not trap entrained oil and you will empty your sump into the system....I have seen 30 gallons of oil dissapear in about one minute due to this problem.......need much more detail yet.....what sort of screw is it etc?????

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: collecting oil in evaporator

    Yes aygul, go and get all the details. I know its Sunday so first thing tomorow.

    Could the present oil saparator is blocked?
    Is there a sight glass in the oil returning line?

    Chemi

Similar Threads

  1. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  2. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  3. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Replies: 7
    Last Post: 20-03-2006, 02:26 PM
  4. Change evaporator
    By tralex in forum Fundamentals
    Replies: 6
    Last Post: 29-12-2005, 07:53 PM
  5. oil collecting in evaporator
    By EarlH in forum Trouble Shooting
    Replies: 6
    Last Post: 19-03-2005, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •