13-12-2009, 08:04 PM #1
Danfoss Solenoid Valves
Hello,
I am trying to make a solenoid valve selection from
Danfoss catalogue
link.JPG
As an example let's say i am going to use the valve at the liquid line of a system running with R134a.
The values given at the table related (page 8) are for the conditions of Te:-10 C SH:0 and T1 (the temperature ahead of valve): 25C
Supposing that i have got a Qe of 10 kW. And the conditions for Te and SH are totally different from above mentioned.
How should i be able to choose a valve? There are correction factors at the table given at the very same page but it is only for T1. There are no correction factors for Te and SH.
Thank you for your answers
PS: Sorry for posting the link as image. The site does not let me post URLs yet!
-
13-12-2009, 08:10 PM #2
Re: Danfoss Solenoid Valves
My bad. I could also send the catalogue as an attachment.
Here it is!
By the way it is PAGE 11 not 8DKRCC.PD.BB0.A3.02.pdf
-
14-12-2009, 11:16 AM #3
Re: Danfoss Solenoid Valves
Hello
it's easier if you go the software way on the highway
I posted the link below to the selection software
and there you can input all the conditions you want for all the expansion valves from danfoss, and it shows the correct capacity for any conditions
http://www.danfoss.com/North_America...ls/CoolCat.htm
-
14-12-2009, 08:32 PM #4
Re: Danfoss Solenoid Valves
[QUOTE=DEVIL;170432]Hello
it's easier if you go the software way on the highway
I posted the link below to the selection software
and there you can input all the conditions you want for all the expansion valves from danfoss, and it shows the correct capacity for any conditions
Hi devil!
Thanks, i know the coolcat. But i'm trying to get the idea of what goes on scientifically.
I would be so grateful if you can write your comments on my question after seeing the document i attached.
Cheers
-
15-12-2009, 04:57 AM #5
Re: Danfoss Solenoid Valves
Hi again cool, You are jumping the gun a bit when a system is designed you will know the suction and liquid line sizes that is when you select a liquid line solenoid according to line size the duty of the system and pressure drop in the liquid line which should be kept to a minimum
go to this site its free you just need to sign up when you select download it will ask for your details and read its good reading.
http://www.scribd.com/doc/20982762/R...g-Design-Guide
Regards NormLast edited by Toosh; 15-12-2009 at 05:00 AM. Reason: Spelling
My wife used to say you never listen to a word I say at least I think that what she said
Similar Threads
-
Too dependent on Danfoss Valves
By kelvin_27_84 in forum IndustrialReplies: 8Last Post: 24-01-2009, 08:33 PM -
Danfoss EKC315a ETX Valves
By LesClem in forum Technical DiscussionsReplies: 2Last Post: 14-12-2006, 11:26 PM -
Danfoss AKV10 valves
By David PS in forum FundamentalsReplies: 18Last Post: 28-07-2006, 03:56 AM -
Solenoid Valves
By Reeferjon in forum New TechnologiesReplies: 8Last Post: 25-06-2004, 05:49 PM -
Danfoss AKV Valves
By Budokan in forum Supermarket RefrigerationReplies: 8Last Post: 05-04-2004, 07:20 PM