    Mar 2009
    NZ
    54
    29
    set up of hand expansion valves
    Hi there I would like to know the best way to set up hand expansion valves. Some people say via the frost line and others say using 2 thermometers measuring liquid in vs out.
    3,356
    Re: set up of hand expansion valves
    modvalve if you go into search forums "hand expansion valves" you will find what you want .ie
    best td across coil
    frost pattern on coil after defrost with fans off
    Aug 2005
    5,302
    This is always hard to explain.
    1. You need to know what the coil TD should be and does it include the fan motor heat or is it based only on the coil capacity?
    2. Sometimes people select the HEV (hand expansion valve) based on pipe size and not the intended valve capacity.
    3. Selecting the HEV correctly someone should know how many turns open you would need to get the correct pressure drop across the HEV for the desired flow/capacity.
    4. You also need to understand what the valves do. The essentially balance the flow rates/pressure through multiple coils. Each one may have a slightly different setting. Coils at a higher elevation will be more open than those coils at a lower elevation.
    5. Coils closer to the pumps will be adjusted for higher pressure drop across the HEV.
    Then after all of this, you can fine tune the valve setting by watching the frost pattern on the return bends with fans off. Once the last return bend starts to frost the valve should be reasonably adjusted.
    You can confirm this by measuring the coil TD (air inlet minus air exit temperatures).
    Mar 2009
    NZ
    54
    29
    OK thanks for that unfortunately the hand expansion valves are on the coolstore roof so it takes 10 minutes to reach the evaporators I think I have set them up as best I can 2 turns open
    Nov 2008
    India
    83
    Differnce between water/Brine Temperatur & Suction Temperatur should be 7 Deg C
  1. minisplit run with king valves closed - is it damaged?
    By cadillackid in forum Air Conditioning
    Last Post: 29-10-2009, 12:19 PM
  2. Too dependent on Danfoss Valves
    By kelvin_27_84 in forum Industrial
    Last Post: 24-01-2009, 08:33 PM
  3. Understanding Balance port TX valves
    By Mobbsy in forum Technical Discussions
    Last Post: 23-07-2008, 04:32 AM
  4. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Last Post: 14-04-2008, 01:47 AM
  5. dan foss tx valves
    By fuzzy in forum Trouble Shooting
    Last Post: 02-10-2007, 01:11 PM