    R407C Bubble / Dew Temperatures



    What are the terms dew temperature and bubble temperature for R407C? Regardingly i found some info on them but i can't define which one to use when doing calculations on a system with R407C.

    Thanks in advance!



  2. #2
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: R407C Bubble / Dew Temperatures

    Quote Originally Posted by ice_cold View Post
    What are the terms dew temperature and bubble temperature for R407C? Regardingly i found some info on them but i can't define which one to use when doing calculations on a system with R407C.

    Thanks in advance!
    Hi ice, this makes good reading

    http://www.centrogalileo.it/nuovaPA/...PONT%20Ing.pdf

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: R407C Bubble / Dew Temperatures

    Quote Originally Posted by ice_cold View Post
    What are the terms dew temperature and bubble temperature for R407C? Regardingly i found some info on them but i can't define which one to use when doing calculations on a system with R407C.

    Thanks in advance!

    Think bubble as the point that water bubbles just as it starts to boil or evaporates.

    Think of dew as the point where the liquid starts to drop out of the vapour.

    So R407 with a glide of 6K means that as the refrigerant starts to boil or evaporate it goes through the bubble point (wet) as it evaporates it glides through the 6K range untill all the liquid has evaporated at the dew point (dry).

    Condensing is reversed, as the refrigerant cools to the saturation temp the liquid starts to drop out of the vapour (dew point) then is condenses through the 6K range untill all the vapour has condensed to liquid (bubble point).

    All the best taz.

    .

  4. #4
    Join Date
    Nov 2009
    Location
    world
    Posts
    19
    Rep Power
    0

    Re: R407C Bubble / Dew Temperatures

    toosh, great document. it gets into detail i liked it!
    and taz thank you. that's well said, so understandable for a beginner like me.

  5. #5
    Join Date
    Apr 2008
    Location
    Texas
    Posts
    8
    Rep Power
    0

    Re: R407C Bubble / Dew Temperatures

    Does anyone have an actual P/T chart that reflects the bubble and dew points? how do you account for temperature glide when determining a good condensing temperature?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: R407C Bubble / Dew Temperatures

    Dew and bubble point is used only for calculation of superheat and subcooling.
    For determining condensation and evaporation saturation temperatures and calculation of aproach and TD you should use mean temperature. There are so many tables around. Google it.

  7. #7
    jowel's Avatar
    jowel Guest

    Re: R407C Bubble / Dew Temperatures

    Im just new here in RE, and i have some questions regarding R407C and i hope someone could help me.

    We are experiencing some problem with our 10-ton split type air-conditioning unit serving electrical room. The condenser is located near a furnace and the surrounding temperature around the condensing unit is around 45 to 55 degrees celsius. With the refrigerant R407C, the discharge pressure of the compressor is reaching 26 bars and the unit is tripping on a high pressure cut-off. We are located here in Doha, Qatar, what will be the gain if we switch from R407C to R134A? Will it help? Does using R407C refrigerant on such high ambient temperature has something to do with the tripping?

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: R407C Bubble / Dew Temperatures

    Quote Originally Posted by jowel View Post
    Im just new here in RE, and i have some questions regarding R407C and i hope someone could help me.

    We are experiencing some problem with our 10-ton split type air-conditioning unit serving electrical room. The condenser is located near a furnace and the surrounding temperature around the condensing unit is around 45 to 55 degrees celsius. With the refrigerant R407C, the discharge pressure of the compressor is reaching 26 bars and the unit is tripping on a high pressure cut-off. We are located here in Doha, Qatar, what will be the gain if we switch from R407C to R134A? Will it help? Does using R407C refrigerant on such high ambient temperature has something to do with the tripping?
    26 bars is 61°C mean temperature and if your ambient goes to 55°C when it trips, than that mean your condenser TD is about 6K which is OK.
    Could you relocate condenser unit away from furnace or bring air from colder environment? I suppose that max 50°C would not trip HP switch.
    Last edited by nike123; 18-07-2010 at 12:37 PM.

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. Loss of R407c performance at high temperature
    By SETCURE in forum Refrigerants
    Replies: 2
    Last Post: 06-08-2009, 05:39 PM
  3. bubble temperature?
    By marc5180 in forum Fundamentals
    Replies: 5
    Last Post: 21-08-2007, 02:05 PM
  4. R407c
    By binman54 in forum Refrigerants
    Replies: 3
    Last Post: 16-12-2006, 09:57 PM
  5. R22 vs R407C.....................again!!
    By Abe in forum Air Conditioning
    Replies: 5
    Last Post: 24-07-2003, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •