    Parallel condensers Shell and tube paralle with Evaporative Condenser



    Hi :

    I´m currently working in a refrigeration plant in Argentina, the plant has one tube and shell condenser and a evaporative condenser working in parallel, what caugh my attention is that the evaporative condenser is sitting on the floor and there is not high difference between the evaportive condenser outlet and the shell and tube outlet.

    I know that in order to make them work, we have to raise the evaporative condenser, but the question is how high?

    The evaportive condenser is a SEMCOBAC VXC135, it has an output of 315000 Kcal/h or 366 Kw, working with 35ºC condensation temperature, and the refrigerant is ammonia.



    Thanks in advance.

    Hernan



  2. #2
    Join Date
    Sep 2007
    Location
    Ukraine
    Age
    39
    Posts
    17
    Rep Power
    0

    Re: Parallel condensers Shell and tube paralle with Evaporative Condenser

    The main problem is that we need to balance the condensers, and this is solved by several methods, in your case, you need more specific look at the PID diagram (scheme) of installation.

  3. #3
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Parallel condensers Shell and tube paralle with Evaporative Condenser

    The height of the condenser is not always the issue. You do, however, need at least a 1 meter high liquid drain leg with an inverted trap at the bottom or the liquid drain needs to enter the bottom of the high pressure receiver. The purpose of the liquid column is to build up a pressure head of liquid refrigerant equal or a little greater than the pressure drop through the evap. condenser at design flow. There is almost no pressure drop through the S & T condenser so the outlet pressure will be much higher than the outlet pressure of the evap. therefore there is a very small flow through the evap. cond. unless you provide this pressure increase by means of a liquid column.

Similar Threads

  1. Fabrication of Cooler Tube & Shell Cooler
    By rickyccong in forum Technical Discussions
    Replies: 1
    Last Post: 27-07-2009, 02:25 PM
  2. Stal Water Cooled Shell & Tube Condensers
    By Samarjit Sen in forum Commercial
    Replies: 2
    Last Post: 18-02-2009, 01:46 AM
  3. Replies: 3
    Last Post: 09-09-2008, 04:33 AM
  4. HELP PLZ: Shell & Tube Selection Parameters
    By Mahmoud in forum Fundamentals
    Replies: 5
    Last Post: 01-02-2008, 01:04 AM
  5. ***** parallel compressor rack systems
    By COLD WANG in forum Commercial
    Replies: 30
    Last Post: 20-12-2006, 06:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •