I wanted to install ammonia sensor and alarm system for a cold storage facility. However, it seems there are so many types to choose from. It seems there are electro-chemical, opto-acoustic, infrared, semi-conductor, explosimeter types. Can someone help me as to the difference between them and what they found to be the better ones based on their experience ?
The system we are using in another location is a Cool-Air model LBW-50. Just wanted to find out more first rather than just duplicate the system.
I'm new to the forum and not quite if this is the correct place to put it. So apologies if it is not in the right place.
-
11-12-2009, 05:03 AM #2
Re: Ammonia Sensors and Alarm
Cool air is good and resonable price , reliable .
-
12-12-2009, 02:03 AM #3
Re: Ammonia Sensors and Alarm
Thanks very much for your input, Ranger1.
What about Chillgard ammonia gas monitor ? Has anyone used these before ? Any good ?
I noticed one say it has a Metal oxide semiconductor sensor while the other says it is electrochemical sensing. I'm confused as to what is the difference and which is better in certain applications
-
12-12-2009, 07:11 AM #4
Re: Ammonia Sensors and Alarm
Try Danfoss site , it may have info on what you require .
-
08-03-2010, 02:52 PM #5
Re: Ammonia Sensors and Alarm
I think you should go for Cool Air Lbw-420, because it has the Detection Sensitivity up to 1000 ppm. Moreover , Coll air detectors have metal oxide semiconductors too.
________________________________
________________________________
Commercial Refrigerator
-
18-03-2010, 11:31 PM #6
Re: Ammonia Sensors and Alarm
Yeah, I did finally went for Cool-Air. Thank you.
-
20-03-2010, 11:49 PM #7
Re: Ammonia Sensors and Alarm
I would only use an electrochemical sensor in areas set to be constantly occupied by personnel. The PEL limit for ammonia is 50ppm and the detection has to be reliable below 50ppm. Your first warning should be at 25-35ppm to allow time to evauate the area. Solid state sensors are not as reliable below 50ppm. Solid state is susceptible to spices, vapors, and other gases which could cause a false reading. Honeywell who bought manning, Gfg, CTI, and Draeger are probably the most widely used in the industry for electrochemical. Infrared are expensive and not good for the lower concentrations yet, but have potential.
-
17-04-2010, 06:34 PM #8
Re: Ammonia Sensors and Alarm
Google the Murco website. Pricey but still the best.
I am not always right, but I'm never wrong!
Similar Threads
-
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 23-01-2012, 11:23 PM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Ammonia Containment
By AndrewU in forum NH3Replies: 12Last Post: 18-03-2010, 11:53 PM -
TK alarm 12
By Fridgevan irela in forum TransportReplies: 3Last Post: 30-10-2009, 01:51 PM -
Thermo King SBIII Alarm Code 29???
By ppodsiadlo in forum TransportReplies: 1Last Post: 31-12-2008, 10:04 PM