    Question Ammonia Sensors and Alarm



    I wanted to install ammonia sensor and alarm system for a cold storage facility. However, it seems there are so many types to choose from. It seems there are electro-chemical, opto-acoustic, infrared, semi-conductor, explosimeter types. Can someone help me as to the difference between them and what they found to be the better ones based on their experience ?
    The system we are using in another location is a Cool-Air model LBW-50. Just wanted to find out more first rather than just duplicate the system.
    I'm new to the forum and not quite if this is the correct place to put it. So apologies if it is not in the right place.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia Sensors and Alarm

    Cool air is good and resonable price , reliable .

  3. #3
    Join Date
    Oct 2009
    Location
    Philippines
    Posts
    18
    Rep Power
    0

    Re: Ammonia Sensors and Alarm

    Thanks very much for your input, Ranger1.
    What about Chillgard ammonia gas monitor ? Has anyone used these before ? Any good ?
    I noticed one say it has a Metal oxide semiconductor sensor while the other says it is electrochemical sensing. I'm confused as to what is the difference and which is better in certain applications

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia Sensors and Alarm

    Try Danfoss site , it may have info on what you require .

  5. #5
    Join Date
    Mar 2010
    Location
    UTAH
    Posts
    24
    Rep Power
    0

    Re: Ammonia Sensors and Alarm

    I think you should go for Cool Air Lbw-420, because it has the Detection Sensitivity up to 1000 ppm. Moreover , Coll air detectors have metal oxide semiconductors too.

    ________________________________
    ________________________________
    Commercial Refrigerator

  6. #6
    Join Date
    Oct 2009
    Location
    Philippines
    Posts
    18
    Rep Power
    0

    Re: Ammonia Sensors and Alarm

    Yeah, I did finally went for Cool-Air. Thank you.

  7. #7
    Join Date
    Apr 2009
    Location
    TEXAS
    Age
    49
    Posts
    28
    Rep Power
    0

    Re: Ammonia Sensors and Alarm

    I would only use an electrochemical sensor in areas set to be constantly occupied by personnel. The PEL limit for ammonia is 50ppm and the detection has to be reliable below 50ppm. Your first warning should be at 25-35ppm to allow time to evauate the area. Solid state sensors are not as reliable below 50ppm. Solid state is susceptible to spices, vapors, and other gases which could cause a false reading. Honeywell who bought manning, Gfg, CTI, and Draeger are probably the most widely used in the industry for electrochemical. Infrared are expensive and not good for the lower concentrations yet, but have potential.

  8. #8
    Join Date
    Jun 2007
    Location
    South Africa
    Age
    66
    Posts
    120
    Rep Power
    17

    Re: Ammonia Sensors and Alarm

    Google the Murco website. Pricey but still the best.
    I am not always right, but I'm never wrong!

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Ammonia Containment
    By AndrewU in forum NH3
    Replies: 12
    Last Post: 18-03-2010, 11:53 PM
  4. TK alarm 12
    By Fridgevan irela in forum Transport
    Replies: 3
    Last Post: 30-10-2009, 01:51 PM
  5. Thermo King SBIII Alarm Code 29???
    By ppodsiadlo in forum Transport
    Replies: 1
    Last Post: 31-12-2008, 10:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •