    Compressor with no pressure difference



    I got called to a site last week with an Airedale condensor that that wasn't running. CUHS3.5 HIEM
    Found the system off on LP with a leak on the coil... I fixed the leak and charged the system but when i ran it the suction and discharge pressures stayed the same and didn't alter even though the compressor was running.
    The system kept tripping on LP as well for some reason even though the correct charge was in.

    I closed the liquid line valve to see if it would pump down but nothing.... i then closed the suction valve but the pressures didn't alter.
    The compressor is 3 phase so i swapped two of the phases around thinking it could be running abckwards but again the pressures stayed the same (6 bar R407c)
    I spoke to Airedale who agreed that it must be a compressor issue.

    I returned today to fit the new compressor and a new LP sensor but when i ran it up it seemed to be doing the same.

    Is it possible for a 4way valve to act as a bypass between suction and discharge... i don't think it is but i'm grasping at straws here.

    The only things i can think is either the compressor is running backwards or the 4 way valve is discharging straight to the suction.

    Has anyone come across anything like this before?


    The difference between genius and stupidity is that genius has its limits.

    Marc

  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: Compressor with no pressure difference

    AN old post by Chunk

    Hi Guys.

    I like these compressors alot.easy to change when they do have a fault.

    The main reason for most of the failures is when people forget about the crankcase heater as the majority of these comps are used on outdoor units.
    the other thing is these comps have an internal pressure relief valve that sometimes doesnt re-seat properly once comp has cooled down giving engineers reason to suspect comp is not pumping.A good whack with a spanner usually sorts this
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Compressor with no pressure difference

    Hi Mark,
    Is it a scroll compressor? If so it would over heat fairly quick and eventually cook if running in reverse.
    Why would the unit trip on LP with a suction pressure of 6bar? Are your gauges connected to the suction/discharge local to compressor?
    Yes a 4 way valve can bypass if stuck half way but I would still expect to see a slight press difference.

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Compressor with no pressure difference

    .A good whack with a spanner usually sorts this[/quote]

    I like your style Paul
    Take it it's not a scroll then, do they still use Maneurope comps?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor with no pressure difference

    Quote Originally Posted by VRVIII View Post
    Take it it's not a scroll then, do they still use Maneurope comps?
    Should be a scroll, that's what the S stands for in the model number.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor with no pressure difference

    Quote Originally Posted by superswill View Post
    the other thing is these comps have an internal pressure relief valve that sometimes doesnt re-seat properly once comp has cooled down giving engineers reason to suspect comp is not pumping.A good whack with a spanner usually sorts this
    I find that a rubber hammer leaves less evidence.

    A leaking 4-way can indeed bypass, although there should be some small pressure difference... but as we are in the mood for whacking things, what the hell... its worth a try.

  7. #7
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor with no pressure difference

    Yes the compressor is a scroll, i doubt that the compressor is stuck now since it was only installed new today.

    If the compressor is running backwards can i just swap any of the phases round? I only tried swapping 2 of them round last time.

    The gauges are connected to the suction and liquid service ports, there isn't any internal service ports.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  8. #8
    compressormick's Avatar
    compressormick Guest

    Re: Compressor with no pressure difference

    is there a suction strainer at comp end?

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor with no pressure difference

    Hi, no there isn't a suction strainer
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Compressor with no pressure difference

    Quote Originally Posted by marc5180 View Post
    Yes the compressor is a scroll, i doubt that the compressor is stuck now since it was only installed new today.

    If the compressor is running backwards can i just swap any of the phases round? I only tried swapping 2 of them round last time.

    The gauges are connected to the suction and liquid service ports, there isn't any internal service ports.
    Swapping any 2 phases will reverse the motor direction, does the unit not have a reverse phase protection device? This would verify correct direction providing the wiring after the device is as per the wiring diagram.

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Compressor with no pressure difference

    The noise of the compressor is totally different when running the other way around. You will easily realise whether this is the case.
    And no, the 4-way valve can't cause what you are saying, because you closed the suction valve and the pressure didn't fall.
    Secondly, no LP trip can occur at 6 bar, can it?

    Is the shell warm where the motor is supposed to be? If so, then it could be wither a NRV stuck open or a safety valve blowing by.

  12. #12
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Compressor with no pressure difference

    Hello marc

    Is there any evidence to support (other than your gauges) that the compressor isn't doing its job. Is there no changes in temp around the associated pipework? A temperature difference between suction and discharge on the compressor?
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor with no pressure difference

    Quote Originally Posted by NoNickName View Post
    The noise of the compressor is totally different when running the other way around. You will easily realise whether this is the case.
    And no, the 4-way valve can't cause what you are saying, because you closed the suction valve and the pressure didn't fall.
    Secondly, no LP trip can occur at 6 bar, can it?

    Is the shell warm where the motor is supposed to be? If so, then it could be wither a NRV stuck open or a safety valve blowing by.
    NoNickName, I think the service valves are where the interconnecting pipe work connects to the unit, like a split ac system and not on the actual compressor, so having gauges here will not show what the compressor is seeing.

    Is there anyway you could connect to where the lp switch is? if its one of those small round jobbies with a 1/4" piece of pipe sticking out, could you fit a line tap valve or piercing pliers and then put your gauges on here? (assuming the LP is between the comp and the reversing valve)

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Compressor with no pressure difference

    http://www.modine.com/web_server_con...12_CFCU_UK.pdf

    quoting:

    SERVICE VALVES
    CU./CUH. 1 - 7.5 Units are provided with suction and liquid line shut-off valves fitted with Schrader
    connectors to facilitate connection of a service gauge manifold (except the CUS 5 - 7.5,
    which have no Schrader connection on the suction valve).

    So please recheck it with suction valve closed, if you didn't yet.
    It also says that there may be an optional hot gas bypass valve fitted. I would bet a fiver on it.

  15. #15
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: Compressor with no pressure difference

    I think you guys have covered just about everything. Knowing my luck, if it was my job, I would probably have been supplied with a duff new compresor!!
    If at first you DO succeed, try to hide your astonishment!!

  16. #16
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor with no pressure difference

    Thanks for all the replies guys, i was back there today this morning just finishing off the maintenance that i had started.

    I used a magnet on the 4way valve and could hear the magnet being pulled across, i even tapped it with a rubber hammer.

    I ran the system up and on heating the compressor would run but the suction and discharge pressures stayed the same at 8 bar each ( theres nothing wrong with my gauges since i checked them on another unit). Eventually the compressor would trip on internal overload.

    I then ran the system up in cooling by placing a magnet on the 4way valve and the discharge stayed at around 8bar but the suction kept dropping and eventually cut off on LP.

    The discharge pipe temp going into the 4 way valve got up to 43°C and coming out of the valve was around 35°C. The suction entering and leaving was around 17°C each but the compressor didn't run long enough to take a proper reading.

    The compressor doesn't have sduction and discharge service valves just liquid and suction service ports on the side of the condensor.
    The only other things that could restrict the flow are TXV's but if the cooling TXV was faulty then i would still expect the system to work in heating and vise versa.

    There is no HGB on this system just 2 TXV's with small non return valves, a drier (which i changed) a sight glass, compressor and a 4 way valve.

    If it was just a problem with the system pumping itself down then it should be a relatively easy task but since on heating the compressor doesn't seem to pump has me stumped.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Compressor with no pressure difference

    Sounds like a 4-way valve problem to me.

  18. #18
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Compressor with no pressure difference

    Mark,

    When energizing the 4 way with your magnet you would hear the solenoid clicking but this only opens a small pilot valve allowing gas through to push the plunger across, but the valve also requires a 4 bar pressure difference to push it across.

    Did you charge liquid in the suction line after evacuating? Most scroll compressors have a discharge reed valve that can be damaged by liquid pumping.

    You would really need check suction/discharge pressures at compressor to verify what's happening.
    Last edited by VRVIII; 10-12-2009 at 09:21 PM.

  19. #19
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Compressor with no pressure difference

    i had a similar problem about 2 years ago on a airedale heat pump it had 2 circuits with scrolls and 1 circuit every time it ran it went out on lp and it only had 1 drier ,2 txv and a four way valve, the drier is special it goes both ways and the problem was 1 off the txv on cooling mode it was not openning,so change for new one and it was fine and the only reason i knew it was going out on lp was by checking the break on switch, in heat mode it was fine

  20. #20
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor with no pressure difference

    Quote Originally Posted by VRVIII View Post
    Mark,

    When energizing the 4 way with your magnet you would hear the solenoid clicking but this only opens a small pilot valve allowing gas through to push the plunger across, but the valve also requires a 4 bar pressure difference to push it across.

    Did you charge liquid in the suction line after evacuating? Most scroll compressors have a discharge reed valve that can be damaged by liquid pumping.

    You would really need check suction/discharge pressures at compressor to verify what's happening.
    Yes i charged liquid into the suction and the liquid but i left the crankcase on for a few hours to boil the liquid off.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  21. #21
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Compressor with no pressure difference

    Quote Originally Posted by GHAZ View Post
    i had a similar problem about 2 years ago on a airedale heat pump it had 2 circuits with scrolls and 1 circuit every time it ran it went out on lp and it only had 1 drier ,2 txv and a four way valve, the drier is special it goes both ways and the problem was 1 off the txv on cooling mode it was not openning,so change for new one and it was fine and the only reason i knew it was going out on lp was by checking the break on switch, in heat mode it was fine
    Thats the thing, if it was only doing it in heating or cooling then the expansion device would be the suspect part but it is doing it in both heating and cooling
    The difference between genius and stupidity is that genius has its limits.

    Marc

  22. #22
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Compressor with no pressure difference

    Quote Originally Posted by marc5180 View Post
    Yes i charged liquid into the suction and the liquid but i left the crankcase on for a few hours to boil the liquid off.
    Did you get to the bottom of this fault or did you have to replace the compressor?

    Leaving the crank heater on would only boil off liquid from the compressor, if the suction line was full of liquid this could have damaged the discharge reed valve due to liquid pumping when started.

Similar Threads

  1. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •