    K Definition reqd



    The difference between bubble temperature and dew temperature is the temperature glide, which varies depending on the refrigerant, but is usually between 1k and 8k.?

    I see this value written for superheat also what are we talking here exactly, with this k symbol?

    sparrow


    Always easy on the eye.

  2. #2
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: K Definition reqd

    K = Kelvin si unit of measurement for temperature

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: K Definition reqd

    Kelvin (k) is a measurement of the degree of heat present in relation to absolute 0.

    Centigrade (c) is a measurement of the degree of heat present in relation to the freezing point of water.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: K Definition reqd

    The actual period between degree Celsius and degree Kelvin is identical i.e. a temp differential of 8k = 8c

    Sorry for the fragmentation Sparrow but on first read I only saw definition of k.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: K Definition reqd

    Quote Originally Posted by sparrow View Post
    The difference between bubble temperature and dew temperature is the temperature glide, which varies depending on the refrigerant, but is usually between 1k and 8k.?

    I see this value written for superheat also what are we talking here exactly, with this k symbol?

    sparrow

    Amongest other things K denotes differance in temp.

    So, air on an evap is 0 deg C air off is -10 deg C the differance is 10K or evap temp is o deg C and suction line temp is 10 deg C = 10K.

    K or Kelvin is the SI standard for measuring temp, but we use Celseus or Centigrade. The divisions of K is the same as the divisions of C but C is only a referance to what happens to water at atmospheric pressures.

  6. #6
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: K Definition reqd

    OK, now I thought to myself how can we be talking about Kelvin, when people keep refering to 5k superheat etc etc, this is
    Particularly off putting when I have had to increase any centigrade, values by 273 to be an equal representation on the Kelvin scale, like if i am transposing ti and t2 they always have to have Kelvin as the temp scale so I add the difference. What am i missing here?

    Sparrow
    Always easy on the eye.

  7. #7
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: K Definition reqd

    Quote Originally Posted by sparrow View Post
    OK, now I thought to myself how can we be talking about Kelvin, when people keep refering to 5k superheat etc etc, this is
    Particularly off putting when I have had to increase any centigrade, values by 273 to be an equal representation on the Kelvin scale, like if i am transposing ti and t2 they always have to have Kelvin as the temp scale so I add the difference. What am i missing here?

    Sparrow

    Nearly there.

    Say for example T1 = 0 deg C and T2 = 10 deg C so the differance is 10 Degrees. Differance in temp is 10 deg K.

    We use K to stop us getting confused when talking about Delta T (differance in temp), thats all.
    Scientists use Kelvin because that is the true measure of temp. We use Centigrade or Celsius because that is the
    referance point of water freezing / boiling.

    So 0 deg C and 100 deg C would equal +273 and +373 deg K on the Kelvin scale.



    taz.
    Last edited by taz24; 08-12-2009 at 06:28 PM.

  8. #8
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: K Definition reqd

    Quote Originally Posted by TRASH101 View Post
    Kelvin (k) is a measurement of the degree of heat present in relation to absolute 0.

    Centigrade (c) is a measurement of the degree of heat present in relation to the freezing point of water.
    Say for example T1 = 0 deg C and T2 = 10 deg C so the differance is 10 Degrees. Differance in temp is 10 deg K.

    We use K to stop us getting confused when talking about Delta T (differance in temp), thats all.
    Scientists use Kelvin because that is the true measure of temp. We use Centigrade or Celsius because that is the
    referance point of water freezing / boiling.

    So 0 deg C and 100 deg C would equal +273 and +373 deg K on the Kelvin scale.

    taz. Thanks for your explinations lads I have it now lol, its the little things sometimes cheers.

    sparrow
    Always easy on the eye.

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: K Definition reqd

    Quote Originally Posted by taz24 View Post
    Nearly there.

    Say for example T1 = 0 deg C and T2 = 10 deg C so the differance is 10 Degrees. Differance in temp is 10 deg K.

    We use K to stop us getting confused when talking about Delta T (differance in temp), thats all.
    Scientists use Kelvin because that is the true measure of temp. We use Centigrade or Celsius because that is the
    referance point of water freezing / boiling.

    So 0 deg C and 100 deg C would equal +273 and +373 deg K on the Kelvin scale.



    taz.

    Good explaination taz.
    You should be a trainer!!!

  10. #10
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: K Definition reqd

    Quote Originally Posted by Grizzly View Post
    Good explaination taz.
    You should be a trainer!!!

    There may be hope for me yet

    taz.

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: K Definition reqd

    Well done Taz,

    Now next lesson for class is LMTD when designing evaporators and condensers or selecting airflow over evaps., relating to room RH. And relating to chilled water HX's, and approach temps., condensers what ever.
    This could really solve a lot of issues that guys in the feild get with existing systems that do not perform correctly, usually not designed correctly.
    magoo

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: K Definition reqd

    OK
    LMTD is "log mean temperature difference, "
    You can all chime in any time soon with interprutations and application criteria

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: K Definition reqd

    Quote Originally Posted by Magoo View Post
    OK
    LMTD is "log mean temperature difference, "
    You can all chime in any time soon with interprutations and application criteria
    "Grey matter churning", Can only be calculated if using steady state conditions (?)
    "churning" need to know temps of all inlets and outlets
    Calculate temp differences.
    Look on chart for the answer.
    I sure it is some think like that.

  14. #14
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: K Definition reqd

    Quote Originally Posted by mad fridgie View Post
    "Grey matter churning", Can only be calculated if using steady state conditions (?)
    "churning" need to know temps of all inlets and outlets
    Calculate temp differences.
    Look on chart for the answer.
    I sure it is some think like that.
    dTlm can also be used in quasi-steady processes - basically, as long the the temperature changes are not of rapidly-changing nature.

    You can use dTlm calculations on a heat-pump component, if you like - it will provide interesting information about the condenser & evaporator.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  15. #15
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: K Definition reqd

    Magoo

    LMTD is a derived value to model heat exchange rates for specific values of environmemtal scenarios.

    This is all well and good when the heat exchange has a steady state medium (i.e. a fluid whose thermophysical properties will not change drastically through the HX process) and not a refrigerant (or steam) that changes state during this process.

    When the medium used can change state then the overall heat transfer coefficient must also change for the proportional volumetric distribution of both states within the physical confines of the HX.

    This is the point it then gets confusing. Is this ratio the same as super heat? If so and the mass flow rate remains the same then how can a bifurcation point arise? The mass flow rate must change for that point to exist in a HX with a fixed volume, steady load and stable superheat and the heat transfer coefficient can only change in respect of the pressure/enthalpy and mass flow or am I missing the point.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  16. #16
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: K Definition reqd

    What gets even more tricky with dTlm, is that the original theory does not involve the concept of 'adequate mass charge'.

    Mass charge in a RHVAC system can drastically modify the dTlm response of a heat-exchanger, from the assumed design value.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  17. #17
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: K Definition reqd

    the original theory does not involve the concept of 'adequate mass charge'
    DesA

    please expand on original theory

    adequate mass charge implicates the full system rather than HX solely
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  18. #18
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: K Definition reqd

    Quote Originally Posted by TRASH101 View Post
    DesA
    please expand on original theory
    adequate mass charge implicates the full system rather than HX solely
    Heat-transfer theory in the derivation of dTlm (log mean temperature difference), makes the implicit assumption that 'enough' liquid/refrigerant/vapour, whatever, is in the heat-exchanger/condenser/evaporator to achieve the required/design value.

    In practice, if the incorrect amount of refrigerant is resident in the heat-exchanger during operation, it will actually have a dTlm different to the design (expected) value.

    This can be seen using a low refrigeration charge, where a condenser, for instance, is most certainly not flooding, but runs at a very low dTlm value. As the system mass charge is raised, the dTlm of this condenser will begin to rise (push back) up until a certain point, after which flooding does begin to take place, & condenser surface is overtaken by liquid subcooling. At this point, the dTlm appears to begins to reduce again.

    So, in the end, RHVAC systems are hugely charge-dependent. We see this a lot in air-to-water heat-pumps, for instance, where the mass charge re-distributes itself during the heat-up cycle. The effect of as little as 10g of additional charge (1-1.5%) can be clearly seen in system performance.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Close Control Definition
    By 2aces in forum Air Conditioning
    Replies: 3
    Last Post: 28-01-2009, 10:09 PM
  2. Definition for cooler selection
    By PaulL in forum Fundamentals
    Replies: 2
    Last Post: 17-09-2008, 09:41 PM
  3. Definition of a Manager
    By bernard in forum Chit Chat & Service Stories
    Replies: 7
    Last Post: 19-06-2008, 06:37 PM
  4. Engineer Definition
    By botrous in forum Training
    Replies: 26
    Last Post: 14-06-2008, 05:37 AM
  5. VRF outdoor unit TR calulation(Pls help reqd. urgently)
    By rajeshrto in forum Fundamentals
    Replies: 1
    Last Post: 04-04-2008, 10:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •