    Hi,
    (I'm french my english is bad)
    We are building ice for show, we have alarm (E651) on our chiller and our compressor 2 is off.
    I think we need password to reset this alarm.
    I need password and to know how to enter it ..
    Display is a CVM 20.
    Maybe someone can be help us ?
    Thanks !
  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,700
    Rep Power
    46
    Re: compressor problem on climaveneta WRAT/LN 0802
    Quote Originally Posted by groug View Post
    Hi,
    Thanks !
    Welcome groug.
    Alarm E651 = Circuit 2 Safety High Pressure trip.
    Manual reset necessary.
    To clear alarms Press C2
    This clears the alarms for Circuit 2.
    C1 clears Circuit 1.
    I hope this Helps?
    Grizzly
  3. #3
    groug's Avatar
    groug Guest
    When we press C2 alarm clear.. But when we press it again, alarm coming again and comp2 doesn't start.
    Now glycol out : -2 and in : 0,5 cauz only comp1 is working..
    We need comp2 to have -12 to make ice ..
  4. #4
    groug's Avatar
    groug Guest
    We found, it's ok.