    Re: Cascade system Design



    required capacity 10TR
    what is TR?



  2. #2
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Cascade system Design

    Required Capacity 35 KW
    TR - Ton per Refrigeration

    My design capacity is 35 KW

  3. #3
    Join Date
    Jul 2009
    Location
    Illinois
    Posts
    189
    Rep Power
    15

    Re: Cascade system Design

    ssk7899,
    Thank you for the clarification. I have been working on mainly cascade refrigeration for over 15 years, I have worked for one of the major manufacturers here in the states and currently work for one of my former customers. In my experience:
    (1) screw compressors are very uncommon
    (2) Bitzer is an excellent compressor
    (3)it is not necessary to have the first stage compressor larger then the second unles you intend to use it for space cooling as well
    (4) R508B and R404A are common choices currently in the states
    (5) with the above mentioned refrigerants POE oil is recomended
    (6) type of evaporator is dependent on what will come in contact with it, if it is not a corrosive enviornment for the copper evap then that is the less expensive choice.
    (7) as to the capacity of the intermediate condenser I am not sure I understand that question, please clarify.

  4. #4
    Join Date
    Nov 2009
    Location
    India
    Age
    41
    Posts
    32
    Rep Power
    0

    Re: Cascade system Design

    Thanks For your reply,,,

    The Intermediate Condenser i.e
    The inter state condenser cum Evaporater.
    for both R508 and R404 gases.

    Could you help me in one more problem ..that is
    i am desigining ultra low temperature chiller
    Required Capacity 35KW and
    Temperature is -120Deg C.

    For this Shall i use three stage cascade system.
    Could explain me breifly ..how to design it.
    What compressors HP required for it.'
    What the Precautions i need to take.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Cascade system Design

    Answered privately with a solution for the two stage cascade.

    No solution for the three stage cascade.

  6. #6
    Join Date
    Oct 2009
    Location
    kuwait
    Posts
    9
    Rep Power
    0

    Re: Cascade system Design

    hi all

    cascad cycles consisting of two separate cycle connicting by heat exchanger. in high stage or condinsing side you can using any refrigerant (410) because the evaporating temperature will be -30,-40 and this refrigerant have boiling point about -46 C
    and for low side cycle you can use R 23 boiling point for it -80 C


    best regards

    Eng. ShMo
    Attached Files Attached Files

Similar Threads

  1. Cascade Refrigeration System
    By Vincent Yu in forum Fundamentals
    Replies: 72
    Last Post: 16-02-2012, 05:04 AM
  2. Cascade system Design
    By ssk7899 in forum Commercial
    Replies: 0
    Last Post: 07-12-2009, 03:23 PM
  3. R-23 cascade system
    By S.M.Gokhale in forum Industrial
    Replies: 22
    Last Post: 08-08-2009, 08:04 AM
  4. Refrigeration system design
    By sachin9782 in forum Refrigerants
    Replies: 4
    Last Post: 19-11-2008, 08:27 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •