    Problems in r22 chiller design



    Hi
    I have designed a chiller and I am facing problems with low suction pressure
    The design conditions are
    Medium - Water
    Refrigerant - R-22
    Water inlet temp - +11ºC
    Water outlet temp - +6ºC
    Evaporating temp - +1ºC

    Chiller design: Type DX Chiller, Double circuit
    Tube OD: 3/4", 20 Gauge plain copper tubes
    Tube Length: 12 Ft
    No of tubes:380 Nos
    No of pass (refrigerant side):6 Pass (per Circuit)
    No of Pass (Water side):22 Pass
    No of tubes per pass:

    1st pass: 9+9
    2nd pass: 14+14
    3rd pass: 28+28
    4th pass: 31+31
    5th pass: 52+52
    6th pass: 56+56

    The above chiller is designed for 135 TR Capacity, but I am unable to get the desired capacity.
    The suction pressure is very low (Between 2.8 to 3 Kg/Sq Cm) at 6ºC chiller outlet

    The chilled water flow through chiller is 90 Cu mtrs/hr
    Temp diff across the chiller is not more than 3.5ºC

    I request somebody to comment on this and suggest the remedy

    Umesh



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Problems in r22 chiller design

    Hi umesh

    what pressures and temperatures are you measuring?

    Full log please.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Problems in r22 chiller design

    You also have to check the water flow and water pressure drop on the heat exchanger.

    You might have a too small pump.

  4. #4
    fridgy's Avatar
    fridgy Guest

    Re: Problems in r22 chiller design

    Quote Originally Posted by chemi-cool View Post
    You also have to check the water flow and water pressure drop on the heat exchanger.

    You might have a too small pump.
    it could also be the flow rate is too high. not enough dwell time in the evaporator will affect the heat absorbtion, i.e lowering the suction pressure and not achieving a good split. try slowing the CHW pump or restricting the flow to see if it makes a difference. good luck

  5. #5
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Problems in r22 chiller design

    Is it me or does that sound like a lot of passes for a chiller? Your expansion valve would have to be very good to cope with all conditions on a 6 pass chiller circuit. I would suggest a 2 or 3 pass circuit and check your valve sizing.
    The Bridge Keeper
    'Answer me these questions three, n'er the other side ye see.'
    What is your name?
    What is your favourite colour?
    What is your suction superheat?

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Problems in r22 chiller design

    'What is the TX valve superheat?
    magoo

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Problems in r22 chiller design

    Calculated flow on the 135 tr is 83.7 m cub per hour .

    1) probably flow appears to be high v/s design i.e. 90 m cub per hr .

    2) chiller pump heat load is accounted in the design load calculations ?
    3) liquid temp aproaching tex ?
    4) temp at tex bulb ?
    5) temp at comp suction ? High suction superheat .
    6) pr drop in tex valve distributor ?
    7) what is condensing temp ?

  8. #8
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Thumbs down Re: Problems in r22 chiller design

    very intresting subject,but this first poster do not react!no manners.

    Moideen-Dubai

  9. #9
    TitanioMan's Avatar
    TitanioMan Guest

    Re: Problems in r22 chiller design

    Hello Umesh
    from my point of vew
    you do have a lot potential to do your needs with the chiller units, lot of area and tube arrange is OK, on DX chillers the unit is really 1 pass only on water side with maybe 22 buffles (looks a lot for me), this can cause a lot of pressure drop and reduce water velocity contact on tube face (the heat exchange rate is proportional to this velocity), you need to increase suction pressure with more liquid thrue TXV valve and set to 0 °, if you are using pure water do not operate chiller below -1 (3.5 to 3.8 BarG), revise the actual superheat and with temperature you can find if some ice is building inside or need more refrigerant, the ice cause heat transfer deficience

  10. #10
    Join Date
    Oct 2006
    Location
    Mumbai
    Age
    64
    Posts
    5
    Rep Power
    0

    Re: Problems in r22 chiller design

    Hello everybody

    First of all I am very sorry for not replying to your posts, as I was unwell and hospatilized, sorry Mr Moideen.

    Firstly as replied by Hall engineer UK, pl clarify why I have to go for 2 to 3 pass, instead of 6 pass, will it not cause reduction in the per tube velicity and accumulation of oil?

    As mentioned by Mr. DD Koranne, the recommended flow rate by him, of 83.7 cu m /Hr, will cause the temperature difference across of the chiller will increase, the total capacity will not change.

    I have tried setting the expansion valve as suggested by titanio man but there is no change in the suction pressure.

    My problem is the temperature difference is only upto 3.5ºC across the chiller and the suction pressure is not increasing, it goes upto 2.5ºC

    I am unable to understand the proble, as I am not getting the required capacity

    Regards

    Umesh Pradhan

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. york chiller ylcs control logic problems
    By koolkatz in forum Trouble Shooting
    Replies: 2
    Last Post: 04-12-2009, 11:59 AM
  3. chiller problems
    By iceman6869 in forum Technical Discussions
    Replies: 8
    Last Post: 19-11-2009, 07:47 AM
  4. Propylene Chiller Problems
    By Maintenance Man in forum Fundamentals
    Replies: 0
    Last Post: 23-09-2009, 11:50 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •