    Compression vs Absorption system



    can any body give me comparison of the two systems?

    plz explain in both financial and technical terms




    Regards


    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  2. #2
    Join Date
    Jul 2003
    Location
    New Delhi,India
    Age
    58
    Posts
    32
    Rep Power
    0

    Thumbs up Re: Compression vs Absorption system

    Quote Originally Posted by abbasi
    can any body give me comparison of the two systems?
    I hope you are talking about aircondition units.

    Cost wise there is huge difference if you compare the compression and absorption type chiller system.(in India Reciprocating type unit of say 100TR costs Rs.1000000.00 and Aborption unit of same capacity will cost Rs.2400000.00)

    technically both systems are totally apart compression type require another deivce or drive to drive the compressor.

    where as absorption type needs heat source only it may waste heat of foundries, biogas, CNG or steam or even hot water of Elecricity generators( og more than 500MW)

    compresion units works with refrigerant only where as absorption units works with refrigerant and absorber.

    dunham bush's web site explains all about absorption

    Tejbir Singh

    Tejbir Singh
    Last edited by Tejbir Singh; 18-12-2004 at 10:20 AM.

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    861
    Rep Power
    21

    Re: Compression vs Absorption system

    Technicly there are huge differences between the 2 systems :
    A compression cycle uses : a compressor (mechanical action is needed) a condenser , an evaporator and an expansion device . . .
    The refrigerant used in compression cycles in a full chemical composite that his proprieties varies according to his pressure and tempreture , the cycle takes advance of those propreties to produce cold (no such thing called cold , the cold is the substruction of heat from a place ).

    An absorption cycle uses a generator usually need power or a source of heat to heat a solution of Ammonia NH3 or Lithium Bromire L2Br and have a condenser , evaporator and an absorber.
    So the refrigerant used here is a water + additives (NH3) wihch makes the solution that will produce cold according to the evolution of it's propreties in the cycle .

    Ammonia is very toxic and isn't advised to be used in residence and commerce ... Lithium Bromire isn't toxic , it is used nowadays in the minibars in the hotels rooms (ex: Electrolux minibars) .

    Financially an absorption system costs more than a compression one maybe because it is rarely manufactured comparing to the compression systems

    Comfort :
    Absorption systems are noise free
    Compression systems have noises

    Servicing :
    Absorption can be considered as a static system that rarely needs to be serviced and maintained.
    Compression is a dynamic system with moving parts which cause it to need maintenance and servicing periodicly.

    Hope the information were useful for u
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Nov 2008
    Location
    Foshan,Guangdong,China
    Posts
    22
    Rep Power
    0

    Re: Compression vs Absorption system

    we should compare compression,absorption & thermo-electric. compressor system is for home & commercial cooling system. absorption is for industrial cooling system. thermo-electric is for small fridge.

  5. #5
    Join Date
    Aug 2006
    Location
    China
    Age
    54
    Posts
    52
    Rep Power
    18

    Re: Compression vs Absorption system

    compressor system is for home and commercial cooling system?
    It is not correct, compression is also for industrial cooling system, and is used widely.

  6. #6
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Compression vs Absorption system

    Quote Originally Posted by yangchenchen View Post
    compressor system is for home and commercial cooling system?
    It is not correct, compression is also for industrial cooling system, and is used widely.
    *Points up* 2004 you're 4 (Closer to 5) years late

  7. #7
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Compression vs Absorption system

    Compression uses electrical energy Absorption uses heat energy(it can be steam, direct fired, Natural gas etc)

    Absorption in todays context is used where you have surplus steam similar to Paper mills where they have Co generation power plants or where easy availabilty of gaseous fuel like LPG or LNG is available.
    Absorption is basically combination of heat & Mass transfer and has very few moving parts and will be bulkier compared to compression system.
    Heat rejection factor in Compression system is in the order of 1.2 for water cooled system and for Absorption it 1.8 and needs bigger cooling tower compared to Compression system

  8. #8
    Join Date
    Apr 2004
    Location
    Pakistan
    Age
    44
    Posts
    131
    Rep Power
    20

    Re: Compression vs Absorption system

    i know the technical details, i just want financial comparison/feasibility
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Compression vs Absorption system

    I would have thought that after four and a bit years you might have the answers by now
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Compression vs Absorption system

    Can you give capacity and fuel source(steam / diesel / CNG /LPG) for Absorption to enable make a comparison.
    In any case Absorption is feasible only where surplus steam is available.
    For 100 TR Screw Chiller will cost Indian Rs.1800000 , where as Steam fired absorption shall be Rs.2500000 and you need to add boiler cost if captive generation need to be made.Trust this will give you a fair idea.
    As per BEE(Bureau of Energy Efficiency) in their reccommendations suggest to use Vapor Absorption only where Steam is available in surplus typically in CO GEN Plants, Paper Mills where steam is used for process and will be available.

  11. #11
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Compression vs Absorption system

    Quote Originally Posted by Brian_UK View Post
    I would have thought that after four and a bit years you might have the answers by now
    My thoughts exactly, could have wrote a book on the subject.

  12. #12
    Join Date
    Feb 2009
    Location
    Cornwall
    Posts
    9
    Rep Power
    0

    Re: Compression vs Absorption system

    I see its 4 year old but can somebody point in the direction of how an absorbers system works, many thanks

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. absorption system
    By rhvac in forum Industrial
    Replies: 2
    Last Post: 22-06-2006, 12:29 AM
  5. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 04:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •