    Short Cycling



    Hay everyone,

    I have this problem with a Freezer unit.

    In normal operation the the unit will cut in at -18C and cut out at -20C.

    Here is my problem when the temp is -20C and the unit is supposed to be cutout until the temp is -18C but it short cycles a few time until the temp is -18C then a solenoid opens and the compressor starts pulling the room back down to -20C

    I noticed that the solenoid on the outlet side was just frosty and when touched the inlet and outlet of the solenoid the inlet was warm and the outlet was cold.

    Could this mean that the seat in the solenoid is not seated properly as there is some refrigerant bypassing which is causing the unit to short cycle during the period it is supposed to be off.




    thanks



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Short Cycling

    hi ferret 82, it sounds like there is something on the seal on the solinoid valve, so when its closed there is gas leaking through, it needs pumping down strip the valve down clean out, maybe fit a liquid line dryer, + there you go

  3. #3
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: Short Cycling

    is the valve far away from the exp valve ?

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Short Cycling

    Quote Originally Posted by ferret82 View Post
    Hay everyone,

    I have this problem with a Freezer unit.

    In normal operation the the unit will cut in at -18C and cut out at -20C.

    Here is my problem when the temp is -20C and the unit is supposed to be cutout until the temp is -18C but it short cycles a few time until the temp is -18C then a solenoid opens and the compressor starts pulling the room back down to -20C

    I noticed that the solenoid on the outlet side was just frosty and when touched the inlet and outlet of the solenoid the inlet was warm and the outlet was cold.

    Could this mean that the seat in the solenoid is not seated properly as there is some refrigerant bypassing which is causing the unit to short cycle during the period it is supposed to be off.




    thanks
    It could be the valve, you need to pump it down and strip the valve down and then see if the seat is damaged or being kept open by swarf or somthing.

    It only takes a few mins to strip so check it.

    taz.

    .

  5. #5
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Short Cycling

    the fact you have frost when the valve is de energised shows its passing, Pump the unit down clean/replace guts of valve change your drier and you will be good as gold!

Similar Threads

  1. Mitsi Heavy short cycling Issue!
    By Daikin=Overated in forum Air Conditioning
    Replies: 10
    Last Post: 20-09-2008, 11:19 PM
  2. Chiller short cycling
    By cmac in forum Fundamentals
    Replies: 14
    Last Post: 11-06-2008, 03:57 AM
  3. Compressor short cycling....
    By sbessettejr in forum Trouble Shooting
    Replies: 10
    Last Post: 02-04-2007, 05:09 PM
  4. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  5. Walk in Cooler (short cycling)
    By Brandon in forum Trouble Shooting
    Replies: 11
    Last Post: 05-05-2003, 11:43 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •