Results 1 to 6 of 6
  1. #1
    Join Date
    Nov 2009
    Location
    usa
    Age
    39
    Posts
    7
    Rep Power
    0

    Evaporators for milk cooling



    I am trying to determine what type of evaporator would be best for a small (40L max) bulk liquid (milk) cooler.

    There will be a maximum of 17L poured into the refrigerator at one time, to be cooled with an approximate thermal load of 70W. The milk will have to be maintained at approximately 40F for three days.

    I have searched high and low and have come to the conclusion that a direct expansion evaporator (stainless) would be most effective.
    1. Can anyone comment on this speculation?
    2. If this will be an effective solution, where would I find a supplier for such a small evaporator?
    3. Are there many other solutions that would be more effective?

    Thanks for your time and I look forward to the comments.



  2. #2
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: Evaporators for milk cooling

    Plate heat exchanger is best for cooling milk as it can be cleaned in place after the process.
    for your quantity container with jacket wher chilled brine is circulated to cool the milk in the container. after getting cooled you can store the milk in the refrigerator or cold room maintaining 40 degree F

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Evaporators for milk cooling

    dont know about most effective but its a basic straight forward approach,you will need a regulator but i cant rember the name off the top of my head but their are blokes here who work on vats.then trot off to your nearest reputable stainless/sheet metal company,preferably one that has dealt with refrigeration gear.wrap your cylinder in copper and get em to fix in place,fit an outer sleeve with caps,urethane fill with foam.depending on the design of your pot you may need an agitator
    Last edited by lowcool; 03-12-2009 at 05:23 AM.
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Evaporators for milk cooling

    I think your best solution would be to have a water jacket around your milk vat. In this jacket make a copper coil on which ice can be formed.

    When you need cooling, you will need to agitate the milk with some sort of motorised paddle, and to move the water around either with a small water pump or make a spray rail at the bottom of the water jacket through which air is blown.

    This is not as efficient as a dx system but there are no issues with it having to be full of milk before you turn it on, and the ice water will keep the milk cool.

    Many commercial milk cooling tanks work this way.

  5. #5
    kbouwman's Avatar
    kbouwman Guest

    Re: Evaporators for milk cooling

    For this small volume would it work to pour it into 1 gallon jugs or keep it in 5 gallon pails and then put them in a residential refrigerater from your local appliance store?

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Evaporators for milk cooling

    Quote Originally Posted by kbouwman View Post
    For this small volume would it work to pour it into 1 gallon jugs or keep it in 5 gallon pails and then put them in a residential refrigerater from your local appliance store?

    Hi kbouwman,

    A domestic or even a commercial fridge would keep it cool but it wouldn't cool the milk from animal body temperature to the storage temperature quickly enough to stop bacteria from growing too much in the milk, especially as they plan to keep it for three days. 36F would be a better temperature too for a 72 hour storage time.

    Jon

Similar Threads

  1. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  2. Energy saving Glycol filled dry cooler circuits
    By Jasper in forum Technical Discussions
    Replies: 14
    Last Post: 19-06-2008, 02:18 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •