    Hello people. Hope someone can clarify some doubts I have about the operation of the oil reservoir in a parallel compressor rack.
    From what I can see in this rack, the oil reservoir is located between the oil separator (high side) and crankcase oil level controls (low side). According to the rack īs manufacturer manual, return oil system is always kept at a pressure slighty higher than that in the compressors crankcases in order to keep the oil flowing from the reservoir into the compressors. But how can this be? Whenever the oil separator float valve cracks open, the pressure in the reservoir, connecting piping and oil level controls must be the same as the high side, correct? Does this high pressure ever reaches the crankcase or suction manifold? Any comments appreciated.



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Supermarket rack oil reservoir question

    1) oil reservoir will have a pressure reducing valve which will vent the refrigerant to suction line header
    2) oil separator outlet (oil) line will have non-return valve . This line feeds oil to reservoir .

    Trust this will explain .

  3. #3
    Join Date
    May 2009
    Location
    New Zealand
    Age
    46
    Posts
    16
    Rep Power
    0

    Re: Supermarket rack oil reservoir question

    We use a product called "Trax oil" which is a float level controlled, modulating valve with an internal reducing orifice. I have found these to be quite reliable, with a fine tolerance to most copeland compressors! Also a lot less hassel than a pressure regulated oil reseviour or a float valve !

Similar Threads

  1. rack novice question
    By friocold2008 in forum Supermarket Refrigeration
    Replies: 15
    Last Post: 06-12-2009, 10:57 AM
  2. Replies: 1
    Last Post: 02-06-2009, 04:01 PM
  3. question on installation of Hussman supermarket aisle
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 29-07-2008, 01:36 AM
  4. temporary communication failure in supermarket rack controller
    By racktech2008 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 27-04-2008, 09:17 AM
  5. R744 Supermarket Rack
    By 750 Valve in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 28-07-2006, 03:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •