Results 1 to 11 of 11
Thread: nitro purgin
Hybrid View
02-12-2009, 09:28 PM #1
nitro purgin
All the manufactors ask us to nitro purge there pipe work but none give us any flow rates for doing this?? I was told as long as you can feel the nitro comeing out the end of the pipe with the back of your hand that ok.Now that seems a bit old hat doing it like that so does anyone have more info on this ???
02-12-2009, 09:42 PM #2
Re: nitro purgin
Uless you have a flow rate valve how would you
measure the flow anyway.
The acctual rate is 2 ltr a min but unless you can
measure it that is accademic.
So the best way is with a sensative piece of your
skin and make sure all the pipe ends are capped with
just a small vent hole to alow flow.
Cheers taz.
02-12-2009, 09:56 PM #3
Re: nitro purgin
Taz gave as good of an explanation as I can, if not better.
I usually hold my hose to my cheek and feel for the slight flow. Then I hook it up to the piping.
02-12-2009, 10:06 PM #4
Re: nitro purgin
doesnt hurt to have a vertical section at the end either as you know the pipe will fill regardless of your relief hole location
03-12-2009, 04:01 AM #5
Re: nitro purgin
Nitrogen...
Nitro is an abbreviation for nitroglycrine... Won't get me going there, I promise.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
03-12-2009, 04:45 PM #6
03-12-2009, 04:51 PM #7
Re: nitro purgin
You can get those vertical flow meters with a floating bobbin with adjusting screw at the bottom , they are the same type that welders use for mig and tig welding
05-12-2009, 06:37 PM #8
Re: nitro purgin
so 2ltr a min it is then boc sell a flow meter will pick one up .thanks for that taz
05-12-2009, 10:55 PM #9
Re: nitro purgin
Another way is to punch a hole in the rubber or plastic plugs on the tubing. This will vent enough nitrogen through the tubing to keep it clean and you don't need another regulator.
06-12-2009, 10:47 AM #10
Re: nitro purgin
Just use an old service manifold. Use compound side or H.p if you like and set up using hose to pipe or component that your brazing. Set at 5 p.s.i.g ( will vary depending on pipe size) and make sure system is open e.g open service valves or remove pipe caps. Hope this helps
07-12-2009, 09:54 AM #11
Re: nitro purgin
not how i do it, but i red it in a refrigeration book that u ad the other end to a hose and the hose you add it in a bottle of water, and theoretically if u feel once the system with nitrogen, then you just need it to bobble in the water a little bit so you make shore no air is getting back in the system