Re: So Low Ultra low frezeer retrofit
hi there, the problem you will have possibly is the capillary lines as they might required to be changed for the retrofitting. i will have a look in my service manuals and get back to you with the capillary sizes and length and give that a try. for the oil i use as standard mobil eal arctic 22 it is a very good oil to use in the second stage. hope this helps