    Has anyone had problems with charging a system with liquid in the low side of a domestic refrigerator using 134A? I have always been taught and have also read that there is a risk of compressor damage by doing this.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: System charging

    Quote Originally Posted by Dylan
    .....that there is a risk of compressor damage by doing this.
    That's right, there may be the possibility of liquid entering the cylinders and wrecking the compressor.

    It could be argued that the maximum system charge for the fridge/compressor should ensure safe operation but with a cold compressor on start up and charging a risk is there.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2003
    Location
    New Delhi,India
    Age
    58
    Posts
    32
    Rep Power
    0

    Exclamation Re: System charging

    Quote Originally Posted by Dylan
    there is a risk of compressor damage by doing this.
    Yes there is a risk if u dump whole charge in one go. but if you are charging with small quantities then you will not face any problem.As heat generated by Compressor will vaporise the liquid refrigrent.

    Good Practice is to charge with vapours only but in case of blends where refrigerant has to be charged in liquid state only then do the what I have mentioned earlier.

    Tejbir singh

  4. #4
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Re: System charging

    Hi Dylan

    I use a cap-kit ie a copper spun drier with a length of capillary c/w 1/4 brass connection.

    Best regards Mark
    Last edited by Mark; 16-12-2004 at 07:22 PM.

  5. #5
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: System charging

    i use one of those flow reducer things from "yellow jacket" seems to work ok.
    i timed it a couple of days ago, it took 15mins for 600g of 134a.

    cheers

    eggs

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: System charging

    There is a small device called KWIK CHARGE that you connect to the suction line and charge with liquid refrigerant.

    Never used it, only saw it. I believe it made by Imperial of USA.

    Chemi

  7. #7
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,482
    Rep Power
    21

    Re: System charging

    As good practice I always take my time when filling with liquid.

    On the comps I have opened the intake is at the top inside the body and probebly not much chance of completly filling the body with liquid.

    I thought it was that when even a smallish amount of liquid is put in, in boils off and lifts the oil into the pump which can destroy it and not the actual refrigerant liquid.

    Exspeicially when youve already evacuated the system and the oil is ready to absorb most of the charge before it warms up.

    ps any chance of getting a spell checker on this page. cos mine is atrotious
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  8. #8
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: System charging

    just write it full of spelling mistakes and bad grammer, i've only been sort of told off for it once.

    cheers

    eggs

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: System charging

    where's 'quinte'??

    cheers

    richard

  10. #10
    Join Date
    May 2004
    Location
    england
    Age
    63
    Posts
    43
    Rep Power
    0

    Wink Re: System charging

    Use a drier that has a schreader valve fitted ,then charge directly into the liquid line.(NRS)

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: System charging

    Quote Originally Posted by rbartlett
    where's 'quinte'??
    You'll have to learn to Google more, Richard.

    According to the WWW it is in Canada, which I suppose means that it is really somewhere completely different
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 01:39 PM
  4. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  5. Charging a system
    By shark26 in forum Fundamentals
    Replies: 32
    Last Post: 31-01-2006, 07:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •