    Daikin I-touch night set back?



    Customer of ours has a small building with an Itouch. it seems every morning the whole place is set at 18 deg's c when they come in the morning. The offices are cold and the only one who is allowed to operate it doesn't get in till ten..

    We don't know where this setting is and I have looked through the manual and still unsure

    Can anyone give an idiots guide on who/what/where

    Thanks

    Multisync



  2. #2
    Join Date
    Apr 2008
    Location
    england
    Age
    38
    Posts
    41
    Rep Power
    0

    Re: Daikin I-touch night set back?

    From the main screen - have you clicked the little 'S' box for schedule settings?

    I cant actually remember where to go from there though sorry
    Havnt had to sort the schedules out on an iTouch for ages and i forget easy :\

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin I-touch night set back?

    I don't know or use these controllers but looking through the manual
    http://www.daikin.com.sg/manual/VRV_iTouch.pdf (2.89MB)

    Is it anything to do with "Event Setup" which can set the temperatures etc on start or stop.

    Maybe the guy who comes in at 10am is protecting his job position.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Daikin I-touch night set back?

    hi brian thanks for the document we have a site with one of them installed and i never had anything to do with them

    thanks
    lee

  5. #5
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin I-touch night set back?

    Quote Originally Posted by Brian_UK View Post
    I don't know or use these controllers but looking through the manual
    http://www.daikin.com.sg/manual/VRV_iTouch.pdf (2.89MB)

    Is it anything to do with "Event Setup" which can set the temperatures etc on start or stop.

    Maybe the guy who comes in at 10am is protecting his job position.

    I have that manual already via the extranet. I did some training on it many years ago..but that was many years ago

    Thanks any way

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin I-touch night set back?

    Quote Originally Posted by multisync View Post
    Customer of ours has a small building with an Itouch. it seems every morning the whole place is set at 18 deg's c when they come in the morning. The offices are cold and the only one who is allowed to operate it doesn't get in till ten..

    We don't know where this setting is and I have looked through the manual and still unsure

    Can anyone give an idiots guide on who/what/where

    Thanks

    Multisync
    Multisync,

    The night set back function switches the units on when room temp falls below a certain set point this does not adjust the actual set point when units are started (similar to a frost protection). I suspect your problem is that someone has a set a schedule timer to start the units at 18, see below on how to adjust this.

    From the ITC normal display click the bottom right S button
    1.Highlight schedule setup then click execute
    2.Highlight enabled schedule (normally schedule 1)
    then click Enable/disable to disable the schedule prior to modifying.
    3. Click Event Settings (right side 2nd button from top)
    4. Select Monday on top left drop down (all timer schedules for Mon will be shown)
    5. Highlight the first start timer (usually top one) then click the modify button at bottom of screen
    6. You will now see event time (on time) Target units (units to be switched on) etc
    7. Click advanced settings (bottom left button) and you will see a drop down for set temp, this is the set point that the units will be set to at start time. You can set this to the required temp or if you disable the temp set the units will start at the same set point they were when switched off.
    8. You will then need to OK your settings then select Tue..... and repeat above for all days required.

    Good Luck!

  7. #7
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin I-touch night set back?

    You are a Mcstar

  8. #8
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin I-touch night set back?

    No Probs, it might also be worth checking the off timer doesn't have an 18 set point. Let me know you get on.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin I-touch night set back?

    ^^ Well, I was almost there
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Daikin I-touch night set back?

    Is this where you set the day on off's as the client now wants it off sat/sun but allow the employees to override it via the wall mount controller if they are in over the weekend..

  11. #11
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin I-touch night set back?

    Quote Originally Posted by multisync View Post
    Is this where you set the day on off's as the client now wants it off sat/sun but allow the employees to override it via the wall mount controller if they are in over the weekend..
    Yes just delete Sat Sun timer schedules.
    I would also check the last off timer on Friday and verify that R/C mode section has start/stop set to permitted. If this is set to prohibited they will not be able start the unit at the local remote.
    Last edited by VRVIII; 17-12-2009 at 05:34 PM.

Similar Threads

  1. Daikin I Touch controller and VAMs
    By gwilliamson in forum Air Conditioning
    Replies: 4
    Last Post: 15-12-2009, 10:16 PM
  2. DAIKIN intelligent touch controller DCS601C51
    By dr.hankmccoy in forum Air Conditioning
    Replies: 7
    Last Post: 26-06-2009, 09:58 AM
  3. Back inside wall of fridge warm to touch
    By jamstu77@google in forum Domestic
    Replies: 3
    Last Post: 08-12-2007, 08:26 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •