    I am working in Oil & gas sector. We have a refrigeration compressor normally operating at suction pressure of 37/32 (Load/Unload) Kpa. What will be affect on compressor if i operate compressor on very low suction pressures??.. lets say on 15/10 Kpa..
    I know it will enhance the condensate recoveries... but is it suitable for the compressor to operate it on very low suction pressures??
    Please help me...
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Screw Compressor suction pressure
    Model of compressor and refrigerant?
    coolerman's Avatar
    coolerman Guest
    ansar chiller manufacturer and compressör model ?
    Ansar Iqbal Guest
    Model: P200vl-he rotary screw compressor,2950rpm
    refrigerant: Propane
    refrigeration system was designed by propak..
    Thanks for your reply nonickname and coolerman...
    Mar 2006
    Merate (LC) - Italy
    2,549
    Sorry, never heard of it.
    3,355
    Ansar ,
    You can't really damage a screw compressor by runing lower suction pressure .
    It should have all its inbuilt safeties to protect it anyway .
    It looks like a mycom compressor by the numbers you show .
    The only thing that may be effected is oil and discharge temprature , depending what type of oil cooling .
    ie water cooled , liquid injection .
    Liquid injection would cover extra load .
    Just run it at conditions you want and monitor pressures and tempratures to see what if any differences .
    Does compessor have enough spare capacity to achieve suction pressure you require ?