    Heat-pump mass charge determination



    Below is a picture of a typical mass charge determination run for an a/c system.

    I have superimposed on the evaporator power & compressor power, the condenser output power curve (in red).

    For a heat-pump system, which mass charge would you select, & why?

    Last edited by desA; 30-11-2009 at 05:02 AM.


    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat-pump mass charge determination

    The original test data.

    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat-pump mass charge determination

    Taking this a step further.

    There are, for an a/c system, two 'logical' points to consider:
    1. At COP maximum;
    2. At maximum evaporator performance (Q'e,max).

    For a heat-pump, the condenser output performance (Q'c) seems to continue rising as refrigerant mass charge rises.

    Where should the heat-pump cut-off come?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Heat-pump mass charge determination

    Quote Originally Posted by desA View Post
    Taking this a step further.

    There are, for an a/c system, two 'logical' points to consider:
    1. At COP maximum;
    2. At maximum evaporator performance (Q'e,max).

    For a heat-pump, the condenser output performance (Q'c) seems to continue rising as refrigerant mass charge rises.

    Where should the heat-pump cut-off come?
    Surely there must be some mass charge point at which Q'c tops out?

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat-pump mass charge determination

    Thanks Gary.

    Quote Originally Posted by Gary View Post
    Surely there must be some mass charge point at which Q'c tops out?
    Not according to the chart shown (or in practice, for that matter). It seems that the decision for a heat-pump may not be to cut-&-dried as for an a/c. This is what makes it more difficult.

    Things like condenser SC & evap SH seem to become limiting factors, for consideration, well before a Q'c peak can be observed.

    What makes matters even more complicated is that the performance of the system changes across the heating range. So, practically, a set of these curves needs to be developed at each stage along the heating cycle. For the purposes of this thread, we can take it that the curve shown represents the hottest condition for the heat-pump.
    Last edited by desA; 30-11-2009 at 11:48 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Heat-pump mass charge determination

    It looks as if the condenser output, power input, discharge pressure and subcooling are all going up in unison.

    It would seem there must be some point at which they part ways. In particular I would expect the subcooling to cause a reversal in condenser output as the liquid backs up into the condenser.

  7. #7
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat-pump mass charge determination

    Quote Originally Posted by Gary View Post
    It looks as if the condenser output, power input, discharge pressure and subcooling are all going up in unison.

    It would seem there must be some point at which they part ways. In particular I would expect the subcooling to cause a reversal in condenser output as the liquid backs up into the condenser.
    What I've observed practically, is that towards the top end of this mass-charge scale, the condenser pushes back by raising approach & SC as well. There must obviously be some limit, somewhere, but this seems to be moving towards an unsafe region in terms of compressor operation, for no obvious benefit, as it is already past the point of maximum COP.

    What also happens is that Te,sat rises at the same time - releasing more mass-flow, further feeding into the problem.

    Its like these systems don't have a self-regulating mechanism within reasonable pressure bounds.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Heat-pump mass charge determination

    Where is the point of maximum COP?

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Heat-pump mass charge determination

    Quote Originally Posted by Gary View Post
    Where is the point of maximum COP?
    On the charts above, the point of max EER seems to be at 75% final charge.
    Last edited by desA; 01-12-2009 at 05:29 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Calorex 510 Heat pump question
    By jugglerb in forum Heat Pumps
    Replies: 8
    Last Post: 21-06-2009, 10:49 AM
  2. Heat pump hot water system
    By kiamaian in forum Technical Speculations
    Replies: 4
    Last Post: 16-06-2009, 06:48 AM
  3. Sizing of Heat pump
    By pinkpanther in forum Tools and Calculators
    Replies: 5
    Last Post: 24-05-2009, 08:16 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •