    Something I missed?



    I designed my own heat pump for my house. It's been running now for about 2 years now, but there is one question that I have failed to find an answer to now, and thought that someone here, may have an answer.

    Here's the problem:
    When running in heating, the outdoor (evap) has 7 circuits for the distributor. 3 ton nominal system. R22. Balanced port TXV. According to Sporlan's software, the TXV, distributor, and orifice all work good on paper. I have an un-even frosting pattern on the coil however. I'm wondering now, do I have too many circuits?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Is the frost uneven between circuits (more frost on some circuits than others)? Or is the frost uneven across the circuits (more frost at beginning of circuits than end of circuits)?

    What are the following:

    Evap air in temp
    Evap air out temp
    SST (or low side pressure)
    Suction line temp near evap outlet
    Suction line temp near compressor inlet

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Something I missed?

    I will go for poor soldering of the distributor, some of the tubes are partialy blocked.

    On another thing, I'd go with Marc, air flow through the coil.

    Chemi

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    We can't see it from here. The only way we can "see" a system online is by the description and the temperature measurements.

    Going on the insufficient information given, my guess would be an oversized coil, in which case the evap dT will be very low and the superheat will match the evap TD.
    Last edited by Gary; 13-12-2004 at 04:44 PM.

  5. #5
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Well, air flow seems to be fine, in fact too much (approx 5000 cfm) with an 825 rpm 1/2hp fan motor 26" 4wing 27° pitch. Oversized coil, yes, old 10 ton a/c condensor coil with 7 circuits, and 1 subcooling loop (not used in heating).

    Since it's a heat pump, the outdoor temperature varies much, and affects all the numbers. Seem to notice it most when temperatures get cold outside, and frosting begins on coil.

    Several circuits in the middle of the coil is what is frosting up. There is flow through all circuits, all the time. It's not a no-flow situation in some circuits. Solder job looked great on install, looked down inside, and no visible obstructions in the refrigerant path. Upon running, there is a band of frost the appears in the center two or three circuits. It's not at the bottom, (along the ground where ground moisture may be more abundant) or at the top, but dead in the middle.

    Distributor is pointing downward to lend to proper distribution.

    Moisture and dirt *should* not be present, or any other form of contaimination. Pulled an eight our vacuum on the system at 500 microns when I got it, pressurized with nitrogen. It sat for several years, assembled system purging with nitrogen during brazing process, had another 500 micron vacuum and have suction *filter* and bi-flow liquid filter/drier.

    System mass flow, that's something I have not explored. Can you expound on that?

    Thanks!

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    As I understand it, the outdoor coil is a 10 ton coil with a 3 ton TXV and a 3 ton compressor.

    The coil being grossly oversized, likely the superheat at all of the suction ends as well as at the TXV bulb, will be identical to the TD. IOW, the suction line readings will all be at ambient.
    Last edited by Gary; 13-12-2004 at 10:31 PM.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    I would agree with you, Gary, if the compressor and the outdoor coil were a match using a 3 Ton TEV. That's not to say what you say is impossible just that under my scenario far more likely.

    Provided the TEV has something very close to its factory setting then finding superheat discrepancies between circuits should be a piece of cake. Experimenting with a thermometers position air-side before and after non-frosted and frosted tubes too will provide valuable pointers.

    Does the TEV have a MOP function?

    Given a 10 ton coil and 5000 CFM of airflow, the 3 ton flow of refrigerant will be completely boiled off long before it gets to the other end of the coil, and the suction cannot rise above ambient because there is no (above ambient) heat source to cause it to do so. Therefore all coil outlet superheats should theoretically match the TD.
    Last edited by Gary; 13-12-2004 at 11:26 PM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Hopefully Busman will provide us with temperature measurements so we can see what it is doing.

  9. #9
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    TXV is a Sporlan C-charge head (medium temp refrigeration.)

    No flash gas is present in the liquid line. I have a site glass mounted in the liquid line at mid-point between the air handler, and the outdoor unit. This is outside my kitchen window, so that I can monitor system performance. The only time that bubbles are present, is during restart back to heating after a defrost. That may take 5 minutes for bubbles to clear at that mid-point site glass. There is a second site glass mounted at the inlet of the outdoor TXV. (wont Prof sporlan be happy!) That site glass remains clear almost always because it's at the lowest point in the system. No extra means of subcooling is used in heating mode. It comes directly out of the air handler (second floor) and down into the outdoor unit.

    I have experimented with opening up the TXV to decrease superheat. My thinking was attempting to increase the pressure drop across the nozzel and distributor, as opposed to using the TXV pressure drop. This would also create a higher suction pressure too, which should increase the efficiency of the unit in heating mode. Regardless of TXV superheat setting, the results remained unchanged.
    Side note: coil is clean. It's been washed out, cleaned out, cleaned with Calgon's Nu-Brite, so there "shoud" not be any thing restricting air flow through any part of the coil.

    I will see what other hard data I can gather to see which path to go down next.

    I have a second heat pump on the addition to my house. It is a factory built system. It's an ICP (Arcoaire) 12 SEER unit. The homemade system averaged about 15% higher suction pressure (in psia) than that of the factory system in heating mode.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by busman
    TXV is a Sporlan C-charge head (medium temp refrigeration.)

    No flash gas is present in the liquid line. I have a site glass mounted in the liquid line at mid-point between the air handler, and the outdoor unit. This is outside my kitchen window, so that I can monitor system performance. The only time that bubbles are present, is during restart back to heating after a defrost. That may take 5 minutes for bubbles to clear at that mid-point site glass. There is a second site glass mounted at the inlet of the outdoor TXV. (wont Prof sporlan be happy!) That site glass remains clear almost always because it's at the lowest point in the system. No extra means of subcooling is used in heating mode. It comes directly out of the air handler (second floor) and down into the outdoor unit.

    I have experimented with opening up the TXV to decrease superheat. My thinking was attempting to increase the pressure drop across the nozzel and distributor, as opposed to using the TXV pressure drop. This would also create a higher suction pressure too, which should increase the efficiency of the unit in heating mode. Regardless of TXV superheat setting, the results remained unchanged.
    With that oversized coil, there is no way you can adjust the TXV superheat. Adjustment is futile.


    Quote Originally Posted by busman
    Side note: coil is clean. It's been washed out, cleaned out, cleaned with Calgon's Nu-Brite, so there "shoud" not be any thing restricting air flow through any part of the coil.

    I will see what other hard data I can gather to see which path to go down next.
    If you scroll back a page, you will find a list of temperature measurements. Those temperatures will tell the story.


    Quote Originally Posted by busman
    I have a second heat pump on the addition to my house. It is a factory built system. It's an ICP (Arcoaire) 12 SEER unit. The homemade system averaged about 15% higher suction pressure (in psia) than that of the factory system in heating mode.
    How much does the electricity for that oversized condenser fan motor cost?
    Last edited by Gary; 14-12-2004 at 05:32 AM.

  11. #11
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    With that oversized coil, there is no way you can adjust the TXV superheat. Adjustment is futile.(QUOTE) Gary

    With that said I believe you can get some sort of balance by eliminating 3 of the cap tubes and derating the air flow to about 3000 CFM

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by shogun7
    With that oversized coil, there is no way you can adjust the TXV superheat. Adjustment is futile.(QUOTE) Gary

    With that said I believe you can get some sort of balance by eliminating 3 of the cap tubes and derating the air flow to about 3000 CFM

    Actually, I had the other approach in mind: Leave the coil as is and drop the airflow down to about 1000 CFM, give or take a couple hundred.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Morning gentleman. Is that because with the lower than normal TD the coil is more likely to be flooding than anything else, Gary?
    Almost right. Low TD and superheat to match, but no flooding. With that much heat load it can't flood, even if it is wide open, which it is. It might as well be a cap tube.


    Quote Originally Posted by Marc O'Brien
    You must remember, the TEV being matched to the compressor WILL easily control it's own superheat i.e. act to force an establishement of it's superheat setting by simply closing down until it has dictated the operating TD it requires to see the superheat it desires as superheat, and subcool for that matter, is hugely dependant on final coil TD for its establishment.

    I just want to know the relative superheats of the two circuit types, frosting and non frosting, before we move on. Never assume anything, a possible assumption here is that you have even air flow.
    I'm all for getting lots of temperature measurements.

  14. #14
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    TXV is externally equalized (a must for distributor setups.) I don't recall the exact design temperature that I used. I attempted to try numbers at many different ambients to account for all the different temperatures that the unit would be exposed to.

    I don't "think" oil logging is a problem with this setup. It's the same tubes over and over, and frosting begins just after defrost, almost too soon for it too begin to log any oil.

    I have a set of gauges afixed to the unit. This morning, with an ambient of 36°F, it was running 48psig (24°F SST). No superheat reading available yet. I'm home taking care of kids today (sick wife), so that reading is going to be a little be difficult.

    Will post more info soon. Thanks!

  15. #15
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Something I missed?

    Hi busman.

    At 36F, frost on the outdoor coil is normal.
    I dont know what control your defrost, but you can use a thermostat for controlling the amount of frost.

    At these low ambients, you will have more defrost cycles per hour.

    Chemi

  16. #16
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    I have to say that it is fun watching you convert temperatures for a change, Marc.

    As I see it, the factory superheat setting is more like 7F. Since the saturated mixture is boiling off long before it reaches the bulb, the TXV is "seeing" 12F superheat (equal to TD), and is running wide open in a futile attempt to bring down the superheat.

    I would love to do some experimenting here, but we need temperature readings so that we can do before and after comparisons.

  17. #17
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Something I missed?

    One more thing that comes to mind, busman.

    Is the outdoor fan sucking the air from the coil or pushing it through?

    If it pushes the air through the coil or if it sucks it but it is close to the coil then there is almost no air movement at the centre of the coil

    Chemi

  18. #18
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    I used a balanced port TXV in this application, because I thought it would do a better job of controling the refrigerant in this wild application.

    I will go out and get some pics, and parts list of this setup soon.

  19. #19
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Quote Originally Posted by chemi-cool
    Hi busman.

    At 36F, frost on the outdoor coil is normal.
    I dont know what control your defrost, but you can use a thermostat for controlling the amount of frost.

    At these low ambients, you will have more defrost cycles per hour.

    Chemi
    Frosting I expect. It has a demand defrost control on it to handle defrost when necessary, as opposed to time/temperature/thermostat conventional system. This employs two thermistors that compare ambient with coil temperature, and activates defrost when needed.

    The issue is the imbalance of frosting on the coil between circuits.
    I also have put on a time delay relay that runs the outdoor fan for an extra 2 minutes after compressor shut down to allow warmer air in milder temps to help melt off frost, and prevent the need for more call for defrosts.

  20. #20
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    [QUOTE=busman]Well, air flow seems to be fine, in fact too much (approx 5000 cfm) with an 825 rpm 1/2hp fan motor 26" 4wing 27° pitch. Oversized coil, yes, old 10 ton a/c condensor coil with 7 circuits, and 1 subcooling loop (not used in heating).

    How does one use a 3 ton valve to feed a 10 ton heat exchanger and not starve the coil even if its wide open?
    Seems to me you will never get the proper mass flow to feed all the circuits properly (evenly?) thats why I suggested cutting out some circuits and air flow. He's pumping 5 to 7 tons of air through the coil with 5000 CFM in addition to starving it
    Last edited by shogun7; 15-12-2004 at 03:19 AM.

  21. #21
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Well, it's a 10 ton condensor coil, but if you go by coil face area, it's about close to some of your more garden variety residential systems. I think the way that got 10 tons out of this stinker was moving a huge amount of air, and not really worried about SEER rating.

    I was looking at the feeding characteristics tonight, (but was unable to spend enough time to take temps ) The distributor tubes are off of opposite sides of the distributor, so it kinda rules out blockage on one side of the distributor idea.

    Oh, sorry, it was asked before and I forgot to answer. It's not the original fan motor. I replaced it with a slower RPM motor. The original was a 1 hp 1075 rpm motor. Now I have an 825 rpm 1/2hp motor, with original fan blade. I could get away with a 1/3 hp, but when it comes to the coil frosting up, the motor begins to lag down too much. So, electrical draw is much more appealing. Original 5 Amps, now just under 2.

    As promised here is the stat sheet on the parts:

    Copeland ZR34K1PFV Scroll Compressor
    Sporlan BFBVE body with C charge power head
    Sporlan ASC7 Aux Side connector
    Sporlan 1113-7-1/4 distributor
    Sporlan #3 nozzle for distributor

    Now, here's something that I forgot all about, until I started looking at this thing again tonight. Sporlan did not offer a 3/16 connection for distributor that I needed. I needed 3/16 according to their program to gain enough pressure drop for a proper operating distributor. So, I used a 1/4 distributor. I used 1/4" tubing stubs, exactly cut, fitted the 3/16's into the 1/4" tubing, at exact insertations, (so all would be equal). The other part that I noticed, was I had to use an ASC7 (7/8) connector to fit the distributor. So, I had to sweat a reducer between the TXV and the ASC.

  22. #22
    peterweston's Avatar
    peterweston Guest

    Re: Something I missed?

    Does the unit ever cylce? Not sure on the temp as i am in Australia and indoor heating not used that often.

  23. #23
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    So have I dropped off my internal coil velocity too far you think?

  24. #24
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Quote Originally Posted by peterweston
    Does the unit ever cylce? Not sure on the temp as i am in Australia and indoor heating not used that often.
    Average wintertime ambient here can range from 25-35°F (sorry guys, I'm stuck on the dumb American system of measurements) over night, which is not too bad. However, last year, was a real bear for this area. Overnight lows were down to about +5°F for about 3 weeks straight. And this heat pump was still heating. Yes, the unit does cycle very well.

  25. #25
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    When are you going to give us some temperature readings, so we can see what this thing is doing?

    Evap air in temp
    Evap air out temp
    SST (or low side pressure)
    Suction line temp near evap outlet
    Suction line temp near compressor inlet

    A measurement is worth a thousand calculations.
    Last edited by Gary; 15-12-2004 at 03:15 PM.

  26. #26
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by busman
    Oh, sorry, it was asked before and I forgot to answer. It's not the original fan motor. I replaced it with a slower RPM motor. The original was a 1 hp 1075 rpm motor. Now I have an 825 rpm 1/2hp motor, with original fan blade. I could get away with a 1/3 hp, but when it comes to the coil frosting up, the motor begins to lag down too much. So, electrical draw is much more appealing. Original 5 Amps, now just under 2.
    What makes you think you are getting 5000 CFM of airflow?

  27. #27
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Okay, here are the winning numbers:

    34°F Ambient Temp
    46#psig Suction Pressure
    (22°F) SSTemp
    32°F Suction Line Temp at compressor
    32°F outlet on a circuit that has known to frost (not during measurement)
    Discharge air temperature 29°F.

    So, looks like about a 5°TD on the coil, running 10°F Superheat.

  28. #28
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by busman
    Okay, here are the winning numbers:

    34°F Ambient Temp
    46#psig Suction Pressure
    (22°F) SSTemp
    32°F Suction Line Temp at compressor
    32°F outlet on a circuit that has known to frost (not during measurement)
    Discharge air temperature 29°F.

    So, looks like about a 5°TD on the coil, running 10°F Superheat.
    34 - 29 = 5F dT
    34 - 22 = 12F TD
    29 - 22 = 7F approach
    32 - 22 = 10F superheat

    So, looks like about a 12F TD on the coil, running 10F superheat.

    I'm surprised that the superheat is 2F below the TD. I would question the instrumentation. But I'm thinking Marc may not agree... LOL
    Last edited by Gary; 15-12-2004 at 11:59 PM.

  29. #29
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Here's an experiment you may want to try:

    Remove the fan blade and flip it over, so that it "backhands" the air. This will greatly reduce the airflow. Then take a new set of readings.

    With a 5F dT, you are not getting 5000 CFM, or anywhere in that neighborhood. By downsizing the motor and RPM you have brought the CFM down almost into the acceptable range.
    Last edited by Gary; 16-12-2004 at 12:02 AM.

  30. #30
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Just to clarify:

    When you measure the change in temperature of a single thing, such as a stream of air, the change is a delta-T or dT.

    When you compare the temperatures of two different things, such as the ambient temperature and the refrigerant temperature, the difference is a TD.

  31. #31
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Instruments? Well, saturated suction back up in the evap is probably even a little higher while the actual temperature within the suction line might even be a little lower

    Otherwise, none of those number surprise me. And my concerns about TEV superheat control conflicting with with the TD ceiling are very real indeed. As ambients drop I expect the compressor capacity loss affecting a reduction in TD to overtake the TEV's superheat setting adjustment by dP/dT ratio.

    But none of these figures will tell us whether we have poor air, refrigerant or turbulence distribution.
    There was no difference between the coil outlet superheat and the compressor inlet superheat. How could there be any significant difference on other circuit outlet superheats?

  32. #32
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Given a substantial reduction in airflow (flipping the blade), this should bring the TXV within its full control range, and circuit outlet superheat differences would then be much more pronounced.

  33. #33
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Dummy, it's only a 10 Ton coil at it's nominal TD. Otherwise, it is just a coil. Until you state the index TD it is just a coil and not yet a coil with a capacity rating.

    If it's a 10 Ton coil with a 15K TD then it's a 3.3 Ton coil at a 5K TD except then with poorer tube turbulence and heat transfer. Possibly even with poorer heat transfer in some circuits over other circuits.
    I know that stupid! Did I say it was doing 10 tons at it's existing conditions? NO! I was referring to the fact that it's surface area was capable of doing 10 tons at std conditions. and it's not a 3ton coil at 5K it's a 10 ton coil doing 3 tons of refrigeration!!! so with all your bulsh** your looking either stupid dumb or fuffering from constipation of the cerebral And don't call me names...Dummy!
    Last edited by shogun7; 16-12-2004 at 03:09 AM.

  34. #34
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Agreed, but only if it isn't a distribution problem caused by the excessive TEV closure by the SH/TD conflict I'm talking about
    Fliping the blade may increase TD but I predict a greater frost problem will develop as it will not make much difference to suction temp as ambient falls This coil is just too big for the application to be efficient but it seem to work for busman in a fashon
    Last edited by shogun7; 16-12-2004 at 04:07 AM.

  35. #35
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    One other thing I noticed. I compared the two running systems tonight when I took the readings. The 12 SEER factory system was running at 40# of suction pressure. I like the higher suction pressure of the homemade one better.

    Counterflow - okay, I know what counterflow means, but counterflow what? Counterflow of air, counterflowing refrigerant, or counterflowing of what?

  36. #36
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    Quote Originally Posted by busman
    One other thing I noticed. I compared the two running systems tonight when I took the readings. The 12 SEER factory system was running at 40# of suction pressure. I like the higher suction pressure of the homemade one better.

    Counterflow - okay, I know what counterflow means, but counterflow what? Counterflow of air, counterflowing refrigerant, or counterflowing of what?
    When you install the coil for counterflow operation,you make the suction connection on the entering air side of the coil. This maintains a temperature difference between the coil surface temperature and the leaving refrigerant temperature. It provides one of the control means for the thermostatic expansion valve. As this temperature difference becomes small, suction header location becomes more important. If you neglect the minor effect of pressure drop in an evaporator, the temperature of the refrigerant is constant. The importance of counterflow operation from a capacity standpoint in a direct expansion coil is far less than in a water coil. In a water coil, there is a major change in the temperature of the water passing through the coil.

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by busman
    One other thing I noticed. I compared the two running systems tonight when I took the readings. The 12 SEER factory system was running at 40# of suction pressure. I like the higher suction pressure of the homemade one better.
    Flip the fan blade and see what happens. Try it, you'll like it.

    I would expect little if any difference in suction pressure. What I expect to change is the superheat.
    Last edited by Gary; 16-12-2004 at 06:13 AM.

  38. #38
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    If the low TD is forcing the TEV to take evasive action and close then an increased TD by air flow reduction would allow the valve to open some more.
    Being a medium temp valve, let's imagine that the factory superheat setting is about 7F. The bulb is sensing 10F superheat and is opening as a result. However the saturated mixture is boiling off before reaching the bulb, so the coil stays right there at 10F superheat.

    Given less airflow, I would expect the saturated mixture to then reach the bulb, allowing for 7F superheat. IOW, it would allow the valve to close some more, not open some more.

    BTW, I'm thinking the suction line is in the (lower temp) discharge air stream, which would account for lower than ambient suction line temp. This would explain why the superheat does not currently match the TD.

  39. #39
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    I think that the TXV is throttling as it should be. Last year, I do remember experiementing opening up the TXV more, to reduce superheat.

    Now, if I could figure out how to post the pics from the morning. I took some pics of the frosting pattern. I was not as pronouced this morning, as I have seen it before, but you get a general idea of what's happening. Maybe this something I'm just going to have to live with, or not, I don't know. I was unable to take the specific circuit readings this morning, because I had a relay die on it this morning. My switchover relay to allow my hydronic heat to take over Aux heat failed, and would not allow any Aux heat to come on (hydronic or electric backup) Needless to say, the temp was plumiting when I got up this morning when it went into defrost.

    Hopefully, conditions will come around again here pretty soon, for good dewpoint & temp's for making another good batch of frost, so that I can get some good readings.

    I'm a little leary of some of my readings with this thermocouple thermometer. Whenever the instrument gets cold itself, the temperature likes to drift. So I must keep the instrument warm while taking readings in my coat pocket.

    Two pics are: (1) the in the dark photo, soon after defrost, and the (2) photo is just as defrost begins.
    Attached Images Attached Images

  40. #40
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Other pics to check out:
    First, is just a general pic overhead of the unit.
    Second, is the inside of the unit, and a pic of the distributor.

    The unit is a TTA120 Trane.
    Attached Images Attached Images

  41. #41
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    It looks like each circuit does four complete loops, two of which are frosted. All of the refrigerant is boiled off half way through. It will be interesting to see what it looks like with the blade flipped over.

  42. #42
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Indeed, our opinions don't differ on what makes TEV's open or close, right now they simply differ on which scenario this particular TEV rests, whether it will open or close
    Let see Gary says 7*f SH Soooo I would suspect if Busman flipps the the fan and it goes to oh say 5*f it will stay closed ...However if it goes to OH say 10*f it should go open. Do you agree marc??

  43. #43
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    So Gary, we know that the larger the coil surface area of the evaporator, the closer the coil temperature will be to the entering air temperature. (low TD)This happens because of a higher operating coil temperature with a larger coil and the A/C unit would be running higher evaporating (suction) pressures and temperatures. So if we cut the air flow too low it seems to me that the frosting problem will be exiserbated. What say you?

  44. #44
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by shogun7
    So Gary, we know that the larger the coil surface area of the evaporator, the closer the coil temperature will be to the entering air temperature. (low TD)This happens because of a higher operating coil temperature with a larger coil and the A/C unit would be running higher evaporating (suction) pressures and temperatures. So if we cut the air flow too low it seems to me that the frosting problem will be exiserbated. What say you?
    The TXV is running wide open, metering as much refrigerant as its orifice will allow. The refrigerant is entirely vaporized by the time it gets through two of the four loops in each circuit.

    With less airflow, the liquid/vapor mixture will make it further through the circuit before it is entirely vaporized. Given enough airflow reduction, liquid/vapor mixture will make it to the TXV sensing bulb and the TXV will begin to control the flow.

    At that point, all four loops in each circuit will be frosted. IOW, the frost should be evenly distributed over the entire coil.

  45. #45
    Join Date
    Dec 2004
    Location
    Delaware, USA
    Age
    49
    Posts
    27
    Rep Power
    0

    Re: Something I missed?

    Well, something else I would like to throw in the mix here of discussion, is the amount of refrigerant charge. If I slow down the fan speed, [in my mind] it will require more refrigerant to run in colder temperatures. This thing already has a huge amount of refrigerant in it, and to require more, may in milder temps, run a sky high head pressure. It currently runs over 325 head on mild temperature days, and hate to see rise much higher than that.

    When all these holiday engagements slow down, I hope to get some numbers. . .

  46. #46
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Quote Originally Posted by busman
    Well, something else I would like to throw in the mix here of discussion, is the amount of refrigerant charge. If I slow down the fan speed, [in my mind] it will require more refrigerant to run in colder temperatures. This thing already has a huge amount of refrigerant in it, and to require more, may in milder temps, run a sky high head pressure. It currently runs over 325 head on mild temperature days, and hate to see rise much higher than that.

    When all these holiday engagements slow down, I hope to get some numbers. . .
    Turn the fan blade over. You will NOT need more refrigerant.

    Then report the following temps so we can see everything the system is doing:

    Condenser air in temp
    Condenser air out temp
    Saturated condensing temp (from P/T chart)
    Liquid line temp near condenser
    Liquid line temp near metering device

    Evaporator air in temp
    Evaporator air out temp
    Saturated suction temp (from P/T chart)
    Suction line temp near evaporator
    Suction line temp near compressor
    Last edited by Gary; 18-12-2004 at 10:00 PM.

  47. #47
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    BTW, if you are charging by sightglass you are doing it wrong. Yes, I know it's the way everyone does it. Over the past couple decades I have removed more refrigerant from systems than I have put into systems. Everyone overcharges.

  48. #48
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    Slow the airflow down enough for the saturated mixture to reach the sensing bulb. The TXV will pull back from the wide open position, and you won't need nearly as much refrigerant.

  49. #49
    shogun7's Avatar
    shogun7 Guest

    Re: Something I missed?

    Quote Originally Posted by Marc O'Brien
    Effing moron.

    Proximate Genus: Frosting.
    Specific Difference: Uneven between circuits.

    How does your question tackle the specific difference when it doesn't even satisfactorily indicate a proximate genus?
    Oh stick it in your ear you sick baste88 What I find really funny Marc is youve been all over the place with guesses as with Gary has been at least consistant but hey keep guessing you might hit the right solution
    Last edited by shogun7; 19-12-2004 at 03:25 AM.

  50. #50
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Something I missed?

    An entirely plausible theory, and the frost pattern through the center lends credence to the uneven distribution part, however...

    It seems unlikely that the TXV is throttling the refrigerant flow. If a saturated mixture were reaching the sensing bulb, then the (medium temp) TXV could be adjusted through its full range. As I recall, Busman was unable to open up the valve to further drop its superheat.

    With only vapor reaching the sensing bulb, the superheat cannot be adjusted below the TD, although in this case the superheat seems to be slightly below TD, presumably because it is being influenced by the lower ambient surrounding the suction line.

    In any case, the airflow needs to be reduced in order to achieve some rough balance.

    Also, we need to look at the high side numbers, adjust the refrigerant charge, and then see what the numbers say about overall operation, as well as distribution.

    An interesting project, for sure.
    Last edited by Gary; 19-12-2004 at 12:50 PM.