    Exclamation york chiller ylcs control logic problems



    hello, i am looking for information regarding the controls logic used for the york ylcs07255A50yA.
    i have a water cooled chiller that does not have provisions for condensor water, there is no space to connect a condensor water flow switch and there is no monitoring of cond. water temp. if the cond pump is switched off, the chiller runs and trips on a manual reset hp switch.
    this microprocessor does show provisions for condensor fans.

    the chilled water temp. sensor has also been replaced 3 x times from new, the chiller is 2 years old.
    information from our local johnson controls guys are not easy available and not very helpful



  2. #2
    Join Date
    Dec 2008
    Location
    England
    Age
    59
    Posts
    22
    Rep Power
    0

    Re: york chiller ylcs control logic problems

    Could you confirm model no. pls YLCS0725 ?A 50 YA, ?=S standard unit, H high efficiency, A Remote air cooled. Its not impossible you have the wrong EPROM software fitted. Whichever model you have there is no provision for condense flow switch inputs into the controller, I have previoulsy simply wired in series with the chilled flow switch.

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: york chiller ylcs control logic problems

    Quote Originally Posted by koolkatz View Post
    hello, i am looking for information regarding the controls logic used for the york ylcs07255A50yA.
    i have a water cooled chiller that does not have provisions for condensor water, there is no space to connect a condensor water flow switch and there is no monitoring of cond. water temp. if the cond pump is switched off, the chiller runs and trips on a manual reset hp switch.
    this microprocessor does show provisions for condensor fans.

    the chilled water temp. sensor has also been replaced 3 x times from new, the chiller is 2 years old.
    information from our local johnson controls guys are not easy available and not very helpful
    hi there as yorkie stated either u have the wrong eprom or u could just wire in series as done with evaporator flowswitch!!!!
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Clima Roca York Chiller
    By Chinua in forum Air Conditioning
    Replies: 5
    Last Post: 13-04-2011, 07:03 PM
  2. Carrier 30XA Liquid chiller Problems
    By Ed Burris in forum Commercial
    Replies: 7
    Last Post: 13-08-2010, 08:12 PM
  3. chiller problems
    By iceman6869 in forum Technical Discussions
    Replies: 8
    Last Post: 19-11-2009, 08:47 AM
  4. problems with york yaa c chiller
    By paulwild in forum Commercial
    Replies: 4
    Last Post: 21-08-2007, 08:20 PM
  5. Water Chiller Control
    By David PS in forum Air Conditioning
    Replies: 4
    Last Post: 29-08-2006, 11:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •