    Multiple leaks on capillary tube and suction lines



    Hi Forum

    We are a domestic fridge manufacturer and we have experienced a strange problem on a model of our chest freezer.

    The capillary tube and the suction line (also copper) are foamed-in with heat shrink around to keep the pipes in contact (for heat exchange). In this section (under the heat shrink tube), there have appeared many leaks in both the capillary tube as well as the copper suction line. The leaks become worse with time until it is not possible to re-charge the system.

    Can you suggest the cause of this?



  2. #2
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: Multiple leaks on capillary tube and suction lines

    You shouldnt be rechargeing a system with any leaks, however small.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Galvanic corrosion?
    Chemical, pitting corrosion - accelerated under wrap?
    Poor copper tube.

    Go & see my friend at Copper Tube Africa - Dave Machet - he'll see you right with good copper, I'm sure.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  4. #4
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Thanks desA (and Greg)

    The service technicians have reported that they are not able to charge the system, not us.

    desA, I also suspected Galvanic corrosion, but between copper and copper?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Multiple leaks on capillary tube and suction lines

    The question must be - "How clean was the pipework before it was shrink wrapped?"

    Any form of dirt in there will create problems.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by Clk320_Greg View Post
    You shouldnt be rechargeing a system with any leaks, however small.
    This isn't an answer to the question
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    What brand of copper do you use? Copper is not always copper.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Peter and Brian

    The copper is as clean as it comes from the coil, handled by human hands that may or may not be clean after touching food, dirty, etc. We don't assemble wearing gloves nor do we do any pre-cleaning of our copper tubing (is this bad practice not to pre-clean?). So I guess it is moderately clean but I wouldn't put my tounge anywhere near it! Why? Could dirt aggrivate the problem/cause the problem.

    Peter, I am not exactly sure on Brand? I presume you are referring to the grade of copper? I am interested in what you say 'copper not always copper'. Could you expand on this?

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    I've seen copper evaporators which rusted, so there must be some sort of steel in it.
    The heatshrink you use, is this with glue in it? Perhaps this is reacting with it although I use this practice very often myself.

    Rubbing against each other is almost impossible.
    All the causes given by DesA are possible.

    In such a case - I have one for the moment - I'm sending these pieces to the corrosion lab of the University of Gent not so far from me.
    In attachment a Stainless vessel 316 with pure water in it, heated t o+/- 35°C, installed 11 months ago.! (in BW, color file is too big) IN most cases, they can find the cause but it cost of course something.

    Most cap tubes I've seen were welded together with the suction with tin-alloy. Perhaps this tin acts as a sacrifying anode

    Anyhow, you must find the cause of this problem because your reputation will fall with this. Did you had this problems never in the past? Is this a new product? Have you changed recently from copper supplier?
    Attached Files Attached Files
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Multiple leaks on capillary tube and suction lines

    Peter, do they use hypochlorite anywhere near that stainless vessel?

    Does it look a bit like the stainless has got woodworm?

  11. #11
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    To the OP:
    Check for contamination in your assembly system.
    As mentioned - chemicals in the wrap / poor grade copper (use oxygen-free);
    Be careful of tin-copper solders - they can eat copper.
    ***Stray electrical current, passing through the assembly - earthing strap is where?***
    Do you wrap the assembly in cork tape?



    [I think that Peter's problem lies in poor fabrication practice. The stainless shop has mild steel (carbon steel) somewhere in their system. Perhaps the grinder disc, wire brush. It's on the weld stop/starts - from the look of it.
    What about chlorides? Stress-corrosion - but, this would generally show up as porosity, or surface cracks]
    Last edited by desA; 24-11-2009 at 10:03 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by monkey spanners View Post
    Peter, do they use hypochlorite anywhere near that stainless vessel?

    Does it look a bit like the stainless has got woodworm?
    No water was tested for several elements and chlorides were teh most important tested.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    desA

    We don't wrap in cork tape. I have not heard of this. Where / When is it common to use and for what reason?

    I am going to investigate electrical current. I know that it can have a big effect if the materials have a significant potential difference (e.g. copper and aluminum), but I am still puzzled how this can be the case with copper to copper contact!? Plus the fact that this section is inside the foam so there is hardly moisture for galvanic effect to take place?

    I also will look at what chemicals are in the heat shrink tube and maybe this is the culprit.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Can you make some close-up pictures of the problem area? I can show those perhaps once to the Professor and ask his opinion. Try also to find the specs of the heatshrink.
    I doubt galvanic corrosion because you used copper on copper although like I said, even in copper you can have differences in material.

    This is a little bit the same problem http://www.refrigeration-engineer.co...ead.php?t=7555
    http://www.refrigeration-engineer.co...3&d=1175680488
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by keepmecool View Post
    desA
    We don't wrap in cork tape. I have not heard of this. Where / When is it common to use and for what reason?
    Pipe insulating Everseal - Cork Tape - Eastern Polymer Industry Co., Ltd, Thailand.

    Must be a copy of someone's product out there. Seen it on Galantz a/c outdoor units - capillary.

    I am going to investigate electrical current. I know that it can have a big effect if the materials have a significant potential difference (e.g. copper and aluminum), but I am still puzzled how this can be the case with copper to copper contact!? Plus the fact that this section is inside the foam so there is hardly moisture for galvanic effect to take place?
    There are two types of electrical corrosion to consider:
    1. Galvanic corrosion:
    Local corrosion cell, in the presence of water. Slight material differences may be enough to make one sacrificial to the other.
    2. Stray electrical current:
    Small leakage current from compressor, or wiring, through the troubled area, towards the earth, or some other electrical sink/drain whatever.

    Number 2 is a difficult one to locate. Find your power sources, & locate your earths - what lies roughly in-between?
    Try attaching an earthing strap to each line to bleed off stray current - if it exists - observe the effect.

    I also will look at what chemicals are in the heat shrink tube and maybe this is the culprit.
    Will be interesting.

    Could very well be dud copper tube, all along. Porous.
    Last edited by desA; 25-11-2009 at 09:02 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  16. #16
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Multiple leaks on capillary tube and suction lines

    Has anyone thought about the possibility of the porosity being caused from the inside as in the internal system such as system acidity? Or the possibility of galvanic corrosion being caused by this combined with poor quality copper,Aluminium deposits from such thinks as con rods etc. Moisture plus heat plus poe oil a good catylist for acidification.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by oldesky View Post
    ....Or the possibility of galvanic corrosion being caused by this ....
    Then you have chemical corrosion but not galvanic. Galvanic can only exist with 2 different materials.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Thank you for all your relevant and helpful replies.

    I will try to put some photographs up of the leaky copper pipe and capillary.

    The electrical corrosion is going to be a difficult one to diagnose. I will make an investigation and revert back to the forum soon.

    Oldesky: The internal corrosion was very much considered but we eliminated that due to the fact that it would most likely be in parts of the system outside of the heat shrink area.

    My main focus now will be on what else might be in the copper that can cause this corrosion which might be compounded with stray electrical currents.

  19. #19
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Send samples to Natal University (old name), Mechanical Eng dept. Let them have a go.

    Alternatively CSIR.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  20. #20
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Multiple leaks on capillary tube and suction lines

    I was refering to either or, when I was refering to electrically or chemically induced corrosion. I thought it was clear but obviously not. I think, however, it would be better to concentrate on the problem rather than making pedantic corrections on something so obvious.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by oldesky View Post
    ... I thought it was clear but obviously not. ...
    Indeed, if I re-read your phrase, it still remains confusing for me but English is also not my mother tongue you know.

    Blijkbaar is hier iemand serieus op zijn tenen getrapt is much clearer for me but because it's written in Dutch.
    But we're all focusing here on the problem, we just have to avoid misunderstandings.
    Last edited by Peter_1; 19-01-2010 at 12:46 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Help nie op 'n mens se toone te trap nie...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  23. #23
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    Da Sudafrikaans is tog so scoone vo leeze.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  24. #24
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    ^
    Last edited by desA; 01-12-2009 at 10:10 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  25. #25
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Copper brand is Feinrohren. Peter_1: I am battling to get some close up photographs because a digital camera with 12x zoom cannot magnify it sufficiently. I need to get it photographed under a microscope and as soon as I find a place to get this done I will indeed post the pictures. Watch this space...

    des_A: I am also trying the university of KZN via the mech. eng dept...

  26. #26
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by keepmecool View Post
    des_A: I am also trying the university of KZN via the mech. eng dept...
    Good one.

    Also have a chat to Copper Tubes Africa - Dave Machet - in Jhb. He may also be able to direct you to good corrosion chemists.

    Tell him the yarpie from Laos sent you...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  27. #27
    Join Date
    Nov 2009
    Location
    UK
    Posts
    23
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Quote Originally Posted by Peter_1 View Post
    In such a case - I have one for the moment - I'm sending these pieces to the corrosion lab of the University of Gent not so far from me.
    In attachment a Stainless vessel 316 with pure water in it, heated t o+/- 35°C, installed 11 months ago.!
    By "pure" do you mean distilled or deionised water? It's well known that this will eat stainless, especially at elevated temperatures!

  28. #28
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    No, drinkable water flowing to every house here. Water is strict independent controlled different times/day.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  29. #29
    Join Date
    Aug 2009
    Location
    South Africa
    Age
    51
    Posts
    29
    Rep Power
    0

    Re: Multiple leaks on capillary tube and suction lines

    Just an update for all interested...As it turns out, the heatshrink has bromine added as a flame retardant agent which tends to become dissassociated with heat or with time (maybe both) and forms bromic acid with condensation and this pits the copper tubes (both suction and cap tubes)...who would have thought!!

  30. #30
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Multiple leaks on capillary tube and suction lines

    Thanks for the feedback.

    I think that Brian was on that train of thought.

    Glad you've got it sorted out. Always simple, in the end.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  31. #31
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Multiple leaks on capillary tube and suction lines

    This is a real valuable feedback for all of us and it rarely happens someone comes back here with the solution of the problem.
    Thanks, we're again a little bit wiser.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Replies: 7
    Last Post: 16-11-2010, 11:44 PM
  2. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  3. Replies: 0
    Last Post: 14-05-2008, 05:05 PM
  4. low charge or cap tube blockage ?
    By NC joe in forum Trouble Shooting
    Replies: 8
    Last Post: 12-11-2007, 06:25 AM
  5. The amazing Mr. Cap Tube
    By shogun7 in forum Domestic
    Replies: 52
    Last Post: 07-01-2006, 07:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •