    Angry daikin multi a/c shuts down u4 and a5



    hi i am having problems with my daikin a/con
    it is a 4mk90hvec it is a multi-split system 4 indoor heads into the outdoor unit it has been working for years without a problem then the main room would only come on when you swithched it to fan and when you switch it to cool it shuts off this has been happening for a few months i am getting a u4 error code now the other remaining systems run for about a few hours then they shutt off they have recently been coming up with either u4 or a5 error codes the only way to get them working is shutting the power to the outdoor unit then back on then they work good for another hour or so i don't know a lot about these aircon systems the units have been thoroughly cleaned the led indicators on the outside pcb only one green flashing light that indicates no faults can anyone please help me thanks



  2. #2
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: daikin multi a/c shuts down u4 and a5

    Hi

    E3 means Transmission between indoor and outdoor units the F1 F2 connection terminals check maybe disconnected, wrong or cross wired or Short circuit. Good luck

  3. #3
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: daikin multi a/c shuts down u4 and a5

    Sorry U4 means Transmission problem not E3 as above

  4. #4
    John Parr's Avatar
    John Parr Guest

    Re: daikin multi a/c shuts down u4 and a5

    Quote Originally Posted by 2008_m_clarke View Post
    hi i am having problems with my daikin a/con
    it is a 4mk90hvec it is a multi-split system 4 indoor heads into the outdoor unit it has been working for years without a problem then the main room would only come on when you swithched it to fan and when you switch it to cool it shuts off this has been happening for a few months i am getting a u4 error code now the other remaining systems run for about a few hours then they shutt off they have recently been coming up with either u4 or a5 error codes the only way to get them working is shutting the power to the outdoor unit then back on then they work good for another hour or so i don't know a lot about these aircon systems the units have been thoroughly cleaned the led indicators on the outside pcb only one green flashing light that indicates no faults can anyone please help me thanks
    A U4 fault indicates a communication error between indoor and outdoor and or BS box, A5 is the temperature of the heat exchanger, this may indicate either a faulty sensor or refrigerant shortage, blocked capillaries , reversing valve malfunction (also gas related)

  5. #5
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin multi a/c shuts down u4 and a5

    Quote Originally Posted by 2008_m_clarke View Post
    hi i am having problems with my daikin a/con
    it is a 4mk90hvec it is a multi-split system 4 indoor heads into the outdoor unit it has been working for years without a problem then the main room would only come on when you swithched it to fan and when you switch it to cool it shuts off this has been happening for a few months i am getting a u4 error code now the other remaining systems run for about a few hours then they shutt off they have recently been coming up with either u4 or a5 error codes the only way to get them working is shutting the power to the outdoor unit then back on then they work good for another hour or so i don't know a lot about these aircon systems the units have been thoroughly cleaned the led indicators on the outside pcb only one green flashing light that indicates no faults can anyone please help me thanks
    I would concentrate on the indoor with A5 and check following:

    A5 error (Indoor freeze/overheat protection)

    Supposed causes:

    • Wrong wiring or piping
    • Ev malfunctioning in each room
    • Short-circuit
    • Indoor unit heat exchanger temperature thermistor abnormality
    • Room temperature thermistor abnormality

  6. #6
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: daikin multi a/c shuts down u4 and a5

    Hi clarke
    Well in many cases i've had problem with these old units.
    I recommend to check the outdoor pcb and search for some corrosion states on the components and on the printed areas, on the right side, at the A/B/C/D output / s10. see picture #773.
    If you have u4 on A circuit ( for example ) try to change with another circuit which run well - you can do it on heating mode a few minutes -.
    For a5 you maybe have overheating in heating mode or freeze-up routine in cooling mode, so checkout the filters, the fans, the dirt on the coils and as VRVIII said check also the wiring and the piping one by one... let's say there was a WIRING CORRECTOR button SW3 on the outdoor side ( see picture #769 ) to check the wiring at the first commissioning and then eliminate any wiring error but this will loose information after a power supply failure so check it manualy one by one in cooling mode.
    Good luck
    cool#9
    Attached Images Attached Images

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: daikin multi a/c shuts down u4 and a5

    Sounds like unit has 2 problems.

    Unit is probably miswired which would explain A5 error.

    PCB is getting old and corroded which will give you U4 error, usually on one head only.

    This unit has a wiring correction switch on outdoor. Or alternatively reset unit and run one indoor unit at a time on cooling and see if any of the other units that are turned off have refrigerant flow by listening or feeling the coils with the filters removed.

Similar Threads

  1. Daikin Powers itself up, then shuts down repeatedly
    By Hebden in forum Trouble Shooting
    Replies: 11
    Last Post: 27-03-2010, 02:04 PM
  2. Problem with a daikin multi (please help)
    By airconjohn in forum Trouble Shooting
    Replies: 1
    Last Post: 21-11-2009, 07:28 PM
  3. Panasonic Urban rebadged Daikin
    By complete HVAC in forum Air Conditioning
    Replies: 0
    Last Post: 19-08-2009, 04:35 PM
  4. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  5. Daikin Multi Split A/C problems
    By timholmes204 in forum Air Conditioning
    Replies: 6
    Last Post: 22-05-2008, 12:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •