Results 1 to 12 of 12
  1. #1
    Hebden's Avatar
    Hebden Guest

    Daikin Powers itself up, then shuts down repeatedly



    This units keeps doing this randomly, without any action from the user. Basically turns itself on, runs for 15-60 seconds then shuts down. maybe repeats again in 5-30 mins and just keeps doing that cycle. Any clues?



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Daikin Powers itself up, then shuts down repeatedly

    I think you may have to provide more detail than that.

    Would it not be preferable to call in an expert?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin Powers itself up, then shuts down repeatedly

    Yes, what is the model number ?

    Also, is it a wired remote controller or a hand held? Could be getting interference from other sources.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Hebden's Avatar
    Hebden Guest

    Re: Daikin Powers itself up, then shuts down repeatedly

    Quote Originally Posted by Brian_UK View Post
    Yes, what is the model number ?

    Also, is it a wired remote controller or a hand held? Could be getting interference from other sources.
    hi brian
    4MX80HVEC outdoor unit, using hand held remotes on 3 indoors - they all fire up together when it faults

  5. #5
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: Daikin Powers itself up, then shuts down repeatedly

    Hi

    What error is it showing on the remote controller

  6. #6
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin Powers itself up, then shuts down repeatedly

    Quote Originally Posted by Hebden View Post
    This units keeps doing this randomly, without any action from the user. Basically turns itself on, runs for 15-60 seconds then shuts down. maybe repeats again in 5-30 mins and just keeps doing that cycle. Any clues?
    I would suggest you first check the outdoor unit PCB for signs of corrosion, particularly around the test run button. Units installed in coastal areas have been known to intermittantly start a test run due to the corrosion causing a short circuit. If you find tis is the case I would suggest you replace the PCB and also coat the board with a spray pcb sealant/lacquer.

  7. #7
    Colin Campbell's Avatar
    Colin Campbell Guest

    Re: Daikin Powers itself up, then shuts down repeatedly

    This issue I would say is related to retry's. This type of split system (Multi) is inverter driven and written in the software will be a function that when an error occurs the unit will not automatically generate the error code. It can do up to 16 retry attempts before stopping under error and generating a fault code. The timing between the retry attempts can take up to 30 minutes. If you reset the at all during the retry events, you will reset the error, once it is noted again, the retry function will be re-activated and again you will need to wait for the total amount of retry;s to complete before any code occurs. I suggest that you check the output from the PCB as I would envisage that this error is down to either the compressor or fan motor.

  8. #8
    Gowron's Avatar
    Gowron Guest

    Re: Daikin Powers itself up, then shuts down repeatedly

    Hi Guys, I found this thread whilst searching for faults with Daikin air cons. I'm not a technician but have had exactly this issue with mine. 3 units come on and off together randomly and refuses to turn off with the remotes. I've noticed it seems to happen after electrical storms and resolves by turning the power off at the breaker for 10 minutes and turning it back on. Cheers.

  9. #9
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Daikin Powers itself up, then shuts down repeatedly

    Quote Originally Posted by VRVIII View Post
    I would suggest you first check the outdoor unit PCB for signs of corrosion, particularly around the test run button. Units installed in coastal areas have been known to intermittantly start a test run due to the corrosion causing a short circuit. If you find tis is the case I would suggest you replace the PCB and also coat the board with a spray pcb sealant/lacquer.
    good advice have seen this also

  10. #10
    RRayZz's Avatar
    RRayZz Guest

    Re: Daikin Powers itself up, then shuts down repeatedly

    Hi guys,
    I believe i have the same unit and problem, though im not living in the coastal area. As what Gowron said it happens after electrical storms. However my unit also randomly turns on at night or at certain times of the day. Thus i rang and got a Air condition servicer to have a look, he said this will happen when the weather is humid or damp and concluded that it had some corrosion and we must replace the PCB.
    The company quoted us for $1,203.5AUD to replace the outdoor PCB.
    However its been working fine for about a month now.
    What im want to ask is should i replace it?
    and is $1,203.5 a reasonable price for a PCB or im getting ripped off?
    any thoughts guys?
    Thanks!

  11. #11
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin Powers itself up, then shuts down repeatedly

    Quote Originally Posted by Hebden View Post
    hi brian
    4MX80HVEC outdoor unit, using hand held remotes on 3 indoors - they all fire up together when it faults
    Check that the outdoor unit is wired correctly, Control wires are polarised with the pipework, Have seen these multi splits wired incorrectly several times here.The sparkies who wire them do not realise or are stupid.

  12. #12
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin Powers itself up, then shuts down repeatedly

    yes this will be the outdoor printed circuit board moisture tracking.
    It shorts out the test button on the outdoor unit.
    Replace the outdoor printed circuit board.

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM
  5. Daikin or Mitsubishi
    By eloroncedark in forum Air Conditioning
    Replies: 25
    Last Post: 11-08-2008, 03:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •