    Condensing unit with two coolers



    Hi
    3 hp Condensing unit connected to 20000 btu evaporator in Walk In Cooler. Customer wants to add
    Small Cooler case maybe 4000 btu to the same line.
    I heard that condensing unit should be bypassed to have this setup

    PS
    Thanks Magoo
    I did not put my problem correctly



  2. #2
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Condensing unit with two coolers

    you can bypass the condensing unit if you dont want refrigeration effect.what is your grasp of the term basic commercial condensing unit,mine is compressor+condenser+receiver=simple condensing unit
    mmm to beer or not to beer...........lets drink breakfast

  3. #3
    Join Date
    Nov 2009
    Location
    ny
    Posts
    5
    Rep Power
    0

    Re: Condensing unit with two coolers

    Sorry for my stupidity
    My question is simple
    Some times and maybe more when Walk in Cooler solenoid will close line
    3 HP compressor will push refrigerant to 4000 btu coil ?

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Condensing unit with two coolers

    no it wont the tx valve or similar will create the other pressure drop for refrigerant flow
    mmm to beer or not to beer...........lets drink breakfast

  5. #5
    Join Date
    Nov 2009
    Location
    ny
    Posts
    5
    Rep Power
    0

    Re: Condensing unit with two coolers

    Thank you for replay
    May be I cannot explain clearly
    It is two different evaporators in two different locations
    This system will have big difference in capacity
    Between 20000 btu +4000btu (24000) and 4000
    And compressor on low capacity will starting and stopping continuously
    I am not sure but I think I found answer
    I need discharge bypass valve
    What do you think
    Thank you again

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Condensing unit with two coolers

    YOU NEED A HOT GAS BY PASS VALVE FOR COMPENSATING THE CAPACITY DROP ( DIFFERENCE IN BTUs) . this would ensure that the condensing unit operates on small capacity evaporator . alternatively , you can install a frequency drive . HOWEVER THE LOW CAPACITY EVAPORATOR USING A HIGH CAPACITY COND UNIT WILL RESULT IN OIL RETURN ISSUES .

Similar Threads

  1. Hanging a condensing unit
    By Abe in forum Air Conditioning
    Replies: 19
    Last Post: 01-10-2007, 09:16 PM
  2. Condensing Unit
    By Abe in forum Commercial
    Replies: 0
    Last Post: 09-08-2006, 05:10 PM
  3. Searle Condensing Unit
    By bernard in forum Commercial
    Replies: 1
    Last Post: 01-08-2006, 10:39 PM
  4. DX PAU & Air-cooled condensing unit
    By watana in forum Air Conditioning
    Replies: 6
    Last Post: 27-04-2005, 12:31 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •