Condensing unit with two coolers
Hi
3 hp Condensing unit connected to 20000 btu evaporator in Walk In Cooler. Customer wants to add
Small Cooler case maybe 4000 btu to the same line.
I heard that condensing unit should be bypassed to have this setup
PS
Thanks Magoo
I did not put my problem correctly
-
23-11-2009, 07:21 AM #2
Re: Condensing unit with two coolers
you can bypass the condensing unit if you dont want refrigeration effect.what is your grasp of the term basic commercial condensing unit,mine is compressor+condenser+receiver=simple condensing unit
mmm to beer or not to beer...........lets drink breakfast
-
24-11-2009, 05:04 AM #3
Re: Condensing unit with two coolers
Sorry for my stupidity
My question is simple
Some times and maybe more when Walk in Cooler solenoid will close line
3 HP compressor will push refrigerant to 4000 btu coil ?
-
24-11-2009, 10:55 AM #4
Re: Condensing unit with two coolers
no it wont the tx valve or similar will create the other pressure drop for refrigerant flow
mmm to beer or not to beer...........lets drink breakfast
-
25-11-2009, 03:06 AM #5
Re: Condensing unit with two coolers
Thank you for replay
May be I cannot explain clearly
It is two different evaporators in two different locations
This system will have big difference in capacity
Between 20000 btu +4000btu (24000) and 4000
And compressor on low capacity will starting and stopping continuously
I am not sure but I think I found answer
I need discharge bypass valve
What do you think
Thank you again
-
25-11-2009, 11:50 AM #6
Re: Condensing unit with two coolers
YOU NEED A HOT GAS BY PASS VALVE FOR COMPENSATING THE CAPACITY DROP ( DIFFERENCE IN BTUs) . this would ensure that the condensing unit operates on small capacity evaporator . alternatively , you can install a frequency drive . HOWEVER THE LOW CAPACITY EVAPORATOR USING A HIGH CAPACITY COND UNIT WILL RESULT IN OIL RETURN ISSUES .
Similar Threads
-
Hanging a condensing unit
By Abe in forum Air ConditioningReplies: 19Last Post: 01-10-2007, 09:16 PM -
Condensing Unit
By Abe in forum CommercialReplies: 0Last Post: 09-08-2006, 05:10 PM -
Searle Condensing Unit
By bernard in forum CommercialReplies: 1Last Post: 01-08-2006, 10:39 PM -
DX PAU & Air-cooled condensing unit
By watana in forum Air ConditioningReplies: 6Last Post: 27-04-2005, 12:31 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM