    Question daikin 4mk90hvec problems u4 a5 shutting down



    hi i am having problems with my daikin a/con
    it is a 4mk90hvec it is a multi-split system 4 indoor heads into the outdoor unit it has been working for years without a problem then the main room would only come on when you swithched it to fan and when you switch it to cool it shutts off this has been happening for a few months i am getting a u4 error code now the other remaining systems run for about a few hours then they shutt off they have recently been coming up with either u4 or a5 error codes the only way to get them working is shutting the power to the outdoor unit then back on then they work good for another hour or so i don't know a lot about these aircon systems the units have been thoroughly cleaned the led indicators on the outside pcb only one green flashing light that indicates no faults can anyone please help me thanks



  2. #2
    Join Date
    Aug 2009
    Location
    Mombasa
    Age
    57
    Posts
    27
    Rep Power
    0

    Re: daikin 4mk90hvec problems u4 a5 shutting down

    Hi

    U4 -Malfunction of transmission between indoor and outdoor unit

  3. #3
    Join Date
    Apr 2007
    Location
    Rainham, Essex
    Age
    43
    Posts
    64
    Rep Power
    17

    Re: daikin 4mk90hvec problems u4 a5 shutting down

    Hello

    A9 = Electronic Expansion Valve Drive Error.. Check for power going to the EEV.

    U4 = Comms fault between the Indoor and Outdoor unit..

    All you are doing by switching the system off is making the unit run a diagnostic test on itself. When these faults come up again, you need to see what fault is coming up on the Condenser PCB

  4. #4
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: daikin 4mk90hvec problems u4 a5 shutting down

    Hi,

    A5 error = activation of indoor heat exchanger freeze protection (< 0 oC)

    Checks;
    1. Restriction or recirc of air flow (is the coil clean?)
    2. Shortage of refrigerant
    3. Coil thermistor out of calibration (check resistance/temp 10oC=40kOhms / 20=25kOhms / 25=20kOhms

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Problems with daikin units
    By PRESS in forum Air Conditioning
    Replies: 3
    Last Post: 19-04-2010, 08:10 AM
  3. Daikin RUY5K1Y1 problems!
    By Calais in forum Trouble Shooting
    Replies: 1
    Last Post: 22-11-2009, 12:49 AM
  4. Daikin VRV II problems
    By centrifs in forum Air Conditioning
    Replies: 15
    Last Post: 16-02-2009, 09:33 PM
  5. Daikin Multi Split A/C problems
    By timholmes204 in forum Air Conditioning
    Replies: 6
    Last Post: 22-05-2008, 12:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •