    Carrier 19XR



    I have a Carrier 19XR centrif with high cooler approach which at near full load is around 8-10 degrees F (5-6 degrees C) the oil level looks low in the compressor as well. The skimmer line sight glass was clear. At part load 60% amps and 30% guide vanes the appraoch is much lower (1.3 degrees C or 2.5 degrees F) there is liquid flashing in the skimmer line sight glass and the alert is gone. I checked the resistance of the thermistors which seem OK. The flows are near enough, only marginally low. My deduction is that there is a refrigerant shortage, as at fuller load the liquid in the cooler is below the skimmer line, which leads to poor oil return (the level is lower). Another identical chiller runs mormal oil levels, and a 0.2 degree C appraoch, with flashing in the skimmer line.

    Any other thoughts on this ?


    a problem shared is a problem halved

  2. #2
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Carrier 19XR

    passes the machine and weighs the coolant, pressurized the machine with nitrojeno and locates leakage, verifies be vanishing the fluxes, removed the transducers and verifies that are to atmospheric pressure

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Carrier 19XR

    Theres no real point to weighing out the refrigerant. The name plate is the shipping charge but these machines have their charge trimmed for load conditions. The sensors I checked and calibrated. I have since decided that since the condenser approach is OK and everything other than the evap temp under full load is fine the linear float is stuck.
    a problem shared is a problem halved

  4. #4
    centrifugal's Avatar
    centrifugal Guest

    Re: Carrier 19XR

    Two things will be happen maybe. You loost about 30% of the refrigeration amount or the float valve is blocked.
    In bouth case the machine will run fine till about 70% of load.

  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Carrier 19XR

    I am confident that it will be a float problem. I have not been back since and so I have not taken the float apart

    Thank You
    a problem shared is a problem halved

  6. #6
    Brearmarelm's Avatar
    Brearmarelm Guest

    Carrier 19XR

    Hi Gianni,

    No, Password Carrier does not use the Windows Clipboard to transmit passwords and other sensitive data to the forms.

  7. #7
    Join Date
    Dec 2008
    Location
    Bucharest
    Age
    44
    Posts
    50
    Rep Power
    16

    Re: Carrier 19XR

    Take kare how charge the chiller .If U put too much refrigerant you have the same problem .What time U wait too see oil level ?Need some hours after is start too increase oil level .However the compresor have a small tank where take the oil .

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier 19XR Centrifs
    By wkd in forum Trouble Shooting
    Replies: 13
    Last Post: 27-08-2010, 07:32 PM
  3. Geoff in NY ~ Carrier Parts
    By Futsal1st in forum Trouble Shooting
    Replies: 6
    Last Post: 30-12-2009, 04:07 AM
  4. Carrier 19xr compressor specs
    By caddy in forum Commercial
    Replies: 3
    Last Post: 04-11-2009, 06:33 PM
  5. Carrier 19XR
    By maff in forum Air Conditioning
    Replies: 6
    Last Post: 08-05-2009, 05:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •