    Copeland oil change?



    Hello

    Does anyone know hot to change oil in an copeland zr compressor??

    Havenīt found any document about this on their site nor on internet..

    //Cerwin



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Copeland oil change?

    Which model ZR & what refrigerant?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Copeland oil change?

    I don't think you can. It's an hermetic scroll.

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Copeland oil change?

    Change of oil in ZR series is difficult & not an accurate process. Hence iy is imperative that oil does not get contaminated ; install suction line filters , have a hygenic system , extra precautions during piping etc

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copeland oil change?

    If it has rotalock valves (and is under 7.5 hp as they have a suction strainer) you can remove the suction valve and feed in a thin flexible tube (e.g. silicone tube such as used for fuel lines on model cars or planes) and suck it out with either a syringe or a recovery bottle you have pulled a vacuum in.
    Measure how much came out so you know how much to put back in.
    Or if its a small one you can remove it tip it up so the oil runs out the suction connection.
    On the big 7.5hp ones you can suck the oil out the oil fill connection, once its down to the level of the 1/4" fitting remove it and use the small silicone tube to get the last of the oil out, or tip it over to 45'.

    If its brazed in its more hastle and i think your only option would be to cut the pipework and tip it up, as brazed ones don't usually have oil sightglasses and oil fill ports.

    I have changed the oil in five or six of these so it is possbile

  6. #6
    cerwin's Avatar
    cerwin Guest

    Re: Copeland oil change?

    Hello again

    Got 2 compressors that need oilchange before intalled into other systems.

    one zr61 and one zr48.

    They are both brazed and doesnīt have any oilsightglass.

    so itīs safe to tilt them overnight to drain oil then ?

    going to use poe oil and r134a or r404a havnt desided that one yet

    /Cerwin

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Copeland oil change?

    Quote Originally Posted by cerwin View Post
    Hello again

    Got 2 compressors that need oilchange before intalled into other systems.

    one zr61 and one zr48.

    They are both brazed and doesnīt have any oilsightglass.

    so itīs safe to tilt them overnight to drain oil then ?

    going to use poe oil and r134a or r404a havnt desided that one yet

    /Cerwin
    You have to check first if they are designed for these refrigerants . Pressure wise.

    ZR are for R-22 and for medium temp.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Copeland oil change?

    I have run ZB R404A scrolls on R22 keeping the original poe oil, and ZR R22 scrolls on R407C after changing the oil without problems.
    Don't know about R134a it may depend on your evaporating and condensing temps if the compressor is still in its designed application range.

  9. #9
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Copeland oil change?

    Quote Originally Posted by cerwin View Post
    Hello again

    Got 2 compressors that need oilchange before intalled into other systems.

    one zr61 and one zr48.

    They are both brazed and doesnīt have any oilsightglass.

    so itīs safe to tilt them overnight to drain oil then ?

    going to use poe oil and r134a or r404a havnt desided that one yet

    /Cerwin
    Are these for air-to-water heat-pumps? (A silly question... From Thailand, perhaps)?

    What model of zr48 / zr61? Need to check the shell capability against the refrigerant choice.
    Last edited by desA; 20-11-2009 at 01:38 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  10. #10
    cerwin's Avatar
    cerwin Guest

    Re: Copeland oil change?

    Quote Originally Posted by desA View Post
    Are these for air-to-water heat-pumps? (A silly question... From Thailand, perhaps)?

    What model of zr48 / zr61? Need to check the shell capability against the refrigerant choice.



    One will be water-water groundloop, and the other exhaustair -water.

    the zr serie is designed for 134,407 (The old series of compressors)

    Shell capability?? can u explain this comment


    /Cerwin

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Copeland oil change?

    Shell capability = max pressure. Guys, more and more of you are no more than pirates, loaned to this job, but you shall be kicked out of business with no mercy.
    The max pressure is declared on the label and it's the PS, max safety pressure!!!! It has nothing to do with the shell capability.
    Also, one cannot change the oil to a hermetic, and NO, you're not smart using a straw and making a blow job to suck the oil out. It's not foreseen by the producer? Then you simply CAN'T.

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Copeland oil change?

    ^ Lol...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  13. #13
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Copeland oil change?


    By vacuuming compressor with vacuum pump from discharge side and put one tube of manifold in oil container and connect other one to suction side valve ( compressor ).
    oil goes through manifold to compressor

Similar Threads

  1. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  2. Oil change problem
    By murray75 in forum Technical Discussions
    Replies: 2
    Last Post: 06-02-2009, 07:20 AM
  3. How do you change oil on rotary?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 28-07-2008, 06:05 PM
  4. nitrogen presure/ tempurature change.
    By neil74 in forum Fundamentals
    Replies: 5
    Last Post: 06-03-2008, 10:25 PM
  5. love to hear from the pros.(gas change)
    By jamcool in forum Refrigerants
    Replies: 9
    Last Post: 17-11-2006, 01:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •