Results 1 to 4 of 4
  1. #1
    woonchoon's Avatar
    woonchoon Guest

    what is the diferent for the water chilled and air chilled for the chilled water sys?



    What is the different for the water chilled and air chilled for the chileld water system ? which one is better ? and wht are those advantages ?



  2. #2
    Join Date
    Dec 2009
    Location
    Pakistan
    Age
    61
    Posts
    12
    Rep Power
    0

    Re: what is the diferent for the water chilled and air chilled for the chilled water

    Quote Originally Posted by woonchoon View Post
    What is the different for the water chilled and air chilled for the chileld water system ? which one is better ? and wht are those advantages ?
    As far as I understand thatt you are asking water cooled or air cooled condensing section of chiller?

  3. #3
    Join Date
    Jan 2010
    Location
    Australia
    Posts
    19
    Rep Power
    0

    Re: what is the diferent for the water chilled and air chilled for the chilled water

    Are you referring to the condensing unit which generally classified into air-cooled and water-cooled system?
    Air-cooled is further divided into Air-cooled package and Aircooled split. Whilst the previous has condensing unit and air-conditioning equipment are combined together whereas aircooled split has split up their condensing unit and air conditional equipment.

    Water-cooled chilled system are more complicated as it comprises the condensing unit cooling tower and the air-conditioning equipment.

  4. #4
    Join Date
    Nov 2009
    Location
    Bangladesh
    Age
    37
    Posts
    17
    Rep Power
    0

    Re: what is the diferent for the water chilled and air chilled for the chilled water

    Hi
    Air cool chiller is much much batter then water cool chiller in normal case.Air cool chiller require less space to install,require less electricity,less maintenance,over all more profitable then water cool chiller.But for large cooling load water cool chiller is more profitable.Air cool chiller is batter where cooling laod is less then320 or equal to 320.Over this laod water cool chiller is preferable.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •