    prv's



    hi,

    A customer has a copeland condensing unit with a 11.5 ltr reciever on on it installed in 2007.

    Should a prv have been installed by law?

    Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: prv's

    What do Copeland say and what were the regulations in 2007?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: prv's

    would this be affected by your current refrigerant rules as in not venting to the atmosphere?
    mmm to beer or not to beer...........lets drink breakfast

  4. #4
    Join Date
    Jul 2006
    Location
    uk
    Age
    44
    Posts
    49
    Rep Power
    0

    Re: prv's

    from memory if it has a cooling capacity of 25kw or more then it should have one, they should be recertificated every 5 years under pressure vessel regs.