    I am wondering if there is any way you can test a compressor to see if it is functioning correctly. Not on the electrical side on the refrigeration side to see if it is pumping enough refrigerant though the system.
    Hopefully i have explain this the correct way for you to understand.
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: Compressor Effieiency
    Quote Originally Posted by ferret82 View Post
    Compressor pumping test
    • connect a compound gauge with compressor suction pipe
    • close the compressor suction shut-off valve (should be very tight)
    • Link out L.P. control switch.
    • start the machine to pump down to below 24”Hg.
    • If at least 18”Hg not achieved think valves are defective.
    • If 24 Hg achieved stop compressor& monitor vacuum rise rate. Normal criterion for a new/re-manufactured compressor is not more than 10”/minute.
    (This is only for reciprocating compressors)
    Moideen-Dubai
    Feb 2009
    22
    Thanks for that information, Very handy this site
    Feb 2008
    adelaide sth.oz
    1,015
    checki manufacturers ratings.24 inch is a bit low for me if its hermetic.