    Vacuum specification



    Anybody can venture an opinion !! Does anyone have a definitive spec for the depth of vacuum in a close control unit, My thoughts are 1-2 mbar (750-1500 microns) the local agent for the machine is asking for 400 microns and can't give a valid reason why it has to be so low. Can you help me ?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Vacuum specification

    Because 400 is drier than 750 ??

    Around 1000 micron for AC stuff but you should go lower for refrigeration type levels.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2009
    Location
    idaho
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: Vacuum specification

    500 microns is a good pull the reason being is if you got a tight system youll get that if it leaks you wont.

Similar Threads

  1. Vacuum Pump Questions
    By position1 in forum Fundamentals
    Replies: 7
    Last Post: 08-10-2009, 02:33 AM
  2. Vacuum cleaner as a vacuum pump
    By chemi-cool in forum Chit Chat & Service Stories
    Replies: 18
    Last Post: 14-08-2009, 10:11 PM
  3. Troubleshooting a vacuum pump and gauge set.
    By Old Codger in forum Fundamentals
    Replies: 7
    Last Post: 08-08-2008, 05:13 PM
  4. inverters pulling vacuum
    By bangoman in forum Air Conditioning
    Replies: 2
    Last Post: 05-02-2008, 09:12 PM
  5. Vacuum test
    By Peter_1 in forum Fundamentals
    Replies: 15
    Last Post: 13-10-2006, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •