    Chiller system



    We have chiller unit serving a mortury, the themristors to the elliwell controller, are giving incorrect readings, there is a run out you can change to make the sensors read correct this seems to last a few hours then runs out massivly, the room is currently 4d. inside but the amibent temp is reading 12.

    Can someone please help or advise why this is happening, (please note the cable runs outside the room, around the outer of the building).



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller system

    Probably faulty controller. Connect replacement probe and see if happen again. If yes, then change Eliwell.

    Also, check connection of probe with cable for moisture, and at controller terminals.
    Check controller power supply for correct voltage.
    Last edited by nike123; 13-11-2009 at 10:00 AM.

  3. #3
    Join Date
    Dec 2008
    Location
    Midlands
    Posts
    19
    Rep Power
    0

    Re: Chiller system

    Thanks for the quick reply, that is the exact process we followed, we changed the valve and then the controller.

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller system

    Quote Originally Posted by willetts View Post
    Thanks for the quick reply, that is the exact process we followed, we changed the valve and then the controller.
    And what is outcome?
    Or, after changing both you stil have problem?

  5. #5
    Join Date
    Dec 2008
    Location
    Midlands
    Posts
    19
    Rep Power
    0

    Re: Chiller system

    Yes, the same outcome after chnaging all these elements

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chiller system

    Could there be an Issue with your power supply?
    What is your controller Voltage?

    You may have to check your cable run lengths,
    A simple check would be to use a temporary supply and install the controller nearer the room.
    You should not have to wait long to prove this.
    Good luck and please let us know how you get on.

    Cheers grizzly
    PS. I was going to suggest a dead short, but that would be in bad taste!!!!

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chiller system

    Back again.
    Note PT100 Cable runs can be extended to 100mtrs provided 1.5mmsq cable is used.
    please refer to the attached.
    as possible cause and effect.
    Grizzly

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Chiller system

    Quote Originally Posted by willetts View Post
    Yes, the same outcome after changing all these elements
    And what about this:
    Also, check connection of probe with cable for moisture, and at controller terminals.
    Check controller power supply for correct voltage.
    Then connect these probes directly on controller without extension cable.
    If then works OK you have problem with extension cable type/size, connections, or with EM induction from near power cables.

  9. #9
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Chiller system

    hi
    u can also calibrate the sensor from the parameter sensor calibration or offset hope that help

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Thermobank system from Kramer
    By ardi in forum New Technologies
    Replies: 7
    Last Post: 14-06-2007, 01:00 PM
  3. York chiller system trouble shoot
    By lawrence7435 in forum Trouble Shooting
    Replies: 4
    Last Post: 06-03-2007, 06:54 PM
  4. What is System balance?
    By shogun7 in forum Technical Speculations
    Replies: 56
    Last Post: 19-01-2006, 09:47 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •