Results 1 to 6 of 6
  1. #1
    Join Date
    Sep 2008
    Location
    india
    Age
    39
    Posts
    15
    Rep Power
    0

    Calculation of Heat Transfer Coefficient



    Hi
    I want to design a Heat Exchanger i.e. Condenser .

    Subcooling is 8.3 K
    Condensing Temp 54.4 Deg C
    Ambient Temp is 38 Deg C

    So Temp Difference is (54.4-8)-38=8.4 Deg C
    Heat Rejection is 13.5 KW.
    Copper Tube OD is 3/8" and Thikness is 0.08mm.
    Fan air flow is 1.44 m3/s at 50kpa Pressure Drop .
    Tube Triangular pitch is 25.4 mm
    and Horizontal pitch is 22 mm.

    Please suggest How can i get U value for this .



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Calculation of Heat Transfer Coefficient

    Visit the CoolIt software site & purchase their condenser design program. http://www.coolit.co.za/software.htm

    It's excellent & doesn't cost much at all.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Calculation of Heat Transfer Coefficient

    Sagar the data u hv provided is not sufficient as

    1. Nos of rows and column
    2. Refrigerant

    Provide more data

    Thanks
    Amit

  4. #4
    Join Date
    Sep 2008
    Location
    india
    Age
    39
    Posts
    15
    Rep Power
    0

    Re: Calculation of Heat Transfer Coefficient

    No.of rows are 4 and Refrigerant is R22

  5. #5
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: Calculation of Heat Transfer Coefficient

    What about columns?

  6. #6
    gmavrom's Avatar
    gmavrom Guest

    Re: Calculation of Heat Transfer Coefficient

    let's say that the number of columns is 3 how is the U value calculated?

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. wall heat transfer coefficient measurement
    By Lc_shi in forum Fundamentals
    Replies: 4
    Last Post: 30-10-2006, 01:15 AM

Posting Permissions